color=#0000ff size=2>Question answered.  Thanks, 
everyone.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=418215820-16092009><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=418215820-16092009><FONT face=Arial 
color=#0000ff size=2>Lars Fetzek, EI</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=418215820-16092009><FONT face=Arial 
color=#0000ff size=2>Phoenix Engineering Group</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=418215820-16092009><FONT face=Arial 
color=#0000ff size=2>Tampa, Florida</FONT></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> equest-users-bounces@lists.onebuilding.org 
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Lars 
Fetzek<BR><B>Sent:</B> Wednesday, September 16, 2009 4:48 PM<BR><B>To:</B> 
equest-users@lists.onebuilding.org<BR><B>Subject:</B> [Equest-users] 
SUPPLY-KW/FLOW<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><FONT face=Arial size=2><SPAN class=345183020-16092009>eQuesters & 
DOE2-2ers,</SPAN></FONT></DIV>
<DIV><FONT face=Arial size=2><SPAN 
class=345183020-16092009></SPAN></FONT> </DIV>
<DIV><FONT face=Arial size=2><SPAN class=345183020-16092009>    
The DOE2-2 dictionary loves to use the phrase, "total fan power per unit flow" 
in defining SUPPLY-KW/FLOW.  Clear as mud.</SPAN></FONT></DIV>
<DIV><FONT face=Arial size=2><SPAN class=345183020-16092009>    I 
figured this:  At design conditions, the supply fan runs at 9.90 BHP and 
61.89% efficiency and the per-unit flow is at unity ( x CFM / x CFM = 1).  
The motor nominal efficiency is 93%.  (No, I don't have a motor efficiency 
curve.)  0.746 kW  = 1 HP.  Therefore, the fan kW  =  
9.90 * 0.746 / ( 0.6189 * 0.93 )  =  12.83 kW.  The per unit flow 
is 1.  So... SUPPLY-KW/FLOW  = 12.83, which I type into my .inp 
file.</SPAN></FONT></DIV>
<DIV><FONT face=Arial size=2><SPAN class=345183020-16092009>    
Naturally, eQuest gives me an error message, insisting that SUPPLY-KW/FLOW must 
be between 0.0 and .0080.  Evidently, there is some discrepancy involving 
units or the meaning of "per unit" in the context of the quoted 
phrase.</SPAN></FONT></DIV>
<DIV><FONT face=Arial size=2><SPAN class=345183020-16092009>    
Can anyone clarify what eQuest really means and how to calculate 
SUPPLY-KW/FLOW?  Is it supposed to be KW-per-CFM?</SPAN></FONT></DIV>
<DIV><FONT face=Arial size=2><SPAN class=345183020-16092009>    
Thanks!</SPAN></FONT></DIV>
<DIV><FONT face=Arial size=2><SPAN 
class=345183020-16092009></SPAN></FONT> </DIV>
<DIV><FONT face=Arial size=2><SPAN class=345183020-16092009>Lars Fetzek, 
EI</SPAN></FONT></DIV>
<DIV><FONT face=Arial size=2><SPAN class=345183020-16092009>Phoenix Engineering 
Group</SPAN></FONT></DIV>