<br><font size=2 face="sans-serif">Sara,</font>
<br>
<br><font size=2 face="sans-serif">Sometimes the downloaded weather file
is empty. Go to your Weather/TMY2 folder in the eQuest Data directory
and delete the .bin weather file. When you re-run the simulation,
eQuest will reload the weather file. This should clear up your error.</font>
<br>
<br><font size=2 face="sans-serif">Clayton</font>
<p><font size=3 face="Times New Roman"> </font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td width=40%><font size=1 face="sans-serif"><b>"Lars Fetzek"
<lfetzek@phoenixeng.us></b> </font>
<br><font size=1 face="sans-serif">Sent by: equest-users-bounces@lists.onebuilding.org</font>
<p><font size=1 face="sans-serif">09/15/2009 08:34 AM</font>
<td width=59%>
<table width=100%>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">To</font></div>
<td><font size=1 face="sans-serif">"'Sara Ghalayini'" <sara_ghalayini@yahoo.com>,
<equest-users@lists.onebuilding.org></font>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">cc</font></div>
<td>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">Subject</font></div>
<td><font size=1 face="sans-serif">Re: [Equest-users] simulating building
performance</font></table>
<br>
<table>
<tr valign=top>
<td>
<td></table>
<br></table>
<br>
<br>
<br><font size=2><tt>Sara,<br>
<br>
Though I am not familiar with this error, in particular, my<br>
suggestion for fixing it is the following, which has workwed for some other<br>
errors when I didn't want to start over in the wizard:<br>
<br>
1. Save and close the project. Make a backup in a separate
folder, just in<br>
case the rest of what I suggest fails.<br>
2. Start a new project and use the wizard to set the weather/geographic<br>
location.<br>
3. Save and close the new project.<br>
4. Open the .inp file for the new project in notepad.<br>
5. Copy and paste the weather/geographic lines of code from this
.inp file<br>
to the .inp file in the original project, overwriting the corresponding
data<br>
there.<br>
6. Close the .inp files in notepad.<br>
7. Re-open the modified original project .inp file in eQuest. If
it works<br>
out, save it under a different name/folder and delete the other projects<br>
that have been produced by this procedure.<br>
<br>
Good luck!<br>
<br>
Lars Fetzek, EI<br>
Phoenix Engineering Group<br>
Tamps, Florida<br>
<br>
<br>
-----Original Message-----<br>
From: equest-users-bounces@lists.onebuilding.org<br>
[mailto:equest-users-bounces@lists.onebuilding.org] On Behalf Of Sara<br>
Ghalayini<br>
Sent: Tuesday, September 15, 2009 4:01 AM<br>
To: equest-users@lists.onebuilding.org<br>
Subject: [Equest-users] simulating building performance<br>
<br>
hello,<br>
i finished all the input in equest and resolved all my errors, i wanted
to<br>
simulate building performance and this is the msg that i got: ***error***<br>
End of file read on weather file.<br>
<br>
what does it mean? i can't go back to the first page to change the weather<br>
file anymore.. what should i do?<br>
<br>
thank u<br>
<br>
<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<br>
To unsubscribe from this mailing list send a blank message to<br>
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<br>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<br>
</tt></font>
<br>