<table cellspacing="0" cellpadding="0" border="0" ><tr><td valign="top" style="font: inherit;"><DIV>Hi Greg:</DIV>
<DIV> </DIV>
<DIV>You reached the Nirvana of eQuest information. If my solution isn't the best for you, some other esteemed member will give you his or hers.</DIV>
<DIV> </DIV>
<DIV>Is your server load cooled by DX units or chilled water? If DX, you probably want the server load only satisfied by the DX units, not the other HVAC units in the space. eQuest (DOE-2 engine) cannot have tow systems satisfying one load.</DIV>
<DIV> </DIV>
<DIV>For this situation, I would divide up the room into two zones. The first being the actual space dimensions, mius the server space. In this space, put your DX/chilled water HVAC unit. In the 2nd space, use the server sq.ft and add the server load as Process Load, to be satisfied by the Server HVAC</DIV>
<DIV> </DIV>
<DIV>If your server is cooled by chilled water, I believe it should be the same procedure. However, the process load could be placed directly on the Chilled Water loop as a load. No HVAC required for the server space.</DIV>
<DIV> </DIV>
<DIV>Others may have a more elegant solution.</DIV>
<DIV> </DIV>
<DIV>John Aulbach<BR><BR>--- On <B>Mon, 9/14/09, Ryerson, Gregory <I><Gregory.Ryerson@savvis.net></I></B> wrote:<BR></DIV>
<BLOCKQUOTE style="PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: rgb(16,16,255) 2px solid"><BR>From: Ryerson, Gregory <Gregory.Ryerson@savvis.net><BR>Subject: [Equest-users] Data Center Server Heat Load - 3.63<BR>To: equest-users@lists.onebuilding.org<BR>Date: Monday, September 14, 2009, 7:50 AM<BR><BR>
<DIV id=yiv1106616266>
<STYLE>
<!--
#yiv1106616266
_filtered #yiv1106616266 {font-family:Verdana;panose-1:2 11 6 4 3 5 4 4 2 4;}
#yiv1106616266
#yiv1106616266 p.MsoNormal, #yiv1106616266 li.MsoNormal, #yiv1106616266 div.MsoNormal
        {margin:0in;margin-bottom:.0001pt;font-size:12.0pt;font-family:"Times New Roman";}
#yiv1106616266 a:link, #yiv1106616266 span.MsoHyperlink
        {color:blue;text-decoration:underline;}
#yiv1106616266 a:visited, #yiv1106616266 span.MsoHyperlinkFollowed
        {color:purple;text-decoration:underline;}
#yiv1106616266 span.EmailStyle17
        {font-family:Arial;color:windowtext;}
_filtered #yiv1106616266 {margin:1.0in .5in 1.0in .5in;}
#yiv1106616266 div.Section1
        {}
-->
</STYLE>
<DIV class=Section1>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">I’m a newbie with eQuest and can’t determine how to add server load to my bldg. The ‘Heat Rejection’ and ‘Refrigeration’ sections are all zeroes after a simulation. Where do I add that load so that the HVAC will see the heat load? Thanks, Greg</SPAN></FONT></DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"> </SPAN></FONT></DIV>
<P class=MsoNormal><B><FONT face=Verdana color=#e31937 size=2><SPAN style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: #e31937; FONT-FAMILY: Verdana">Greg Ryerson | Facilities Engineer</SPAN></FONT></B></DIV>
<P class=MsoNormal style="MARGIN-BOTTOM: 6pt"><B><FONT face=Verdana color=#807f83 size=2><SPAN style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: #807f83; FONT-FAMILY: Verdana">Savvis</SPAN></FONT></B></DIV>
<P class=MsoNormal style="MARGIN-BOTTOM: 6pt"><B><FONT face=Verdana color=#807f83 size=2><SPAN style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: #807f83; FONT-FAMILY: Verdana">12301 Tukwila International Blvd</SPAN></FONT></B><B><FONT face=Verdana color=#807f83 size=2><SPAN style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: #807f83; FONT-FAMILY: Verdana">, Tukwila , WA 98168</SPAN></FONT><FONT color=#807f83><SPAN style="COLOR: #807f83"></SPAN></FONT></B></DIV>
<P class=MsoNormal style="MARGIN-BOTTOM: 6pt"><B><FONT face=Verdana color=#807f83 size=2><SPAN style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: #807f83; FONT-FAMILY: Verdana">Office: 206.988.6545 | Mobile: 206.391.5813 | Fax: 206.835.8526</SPAN></FONT></B></DIV>
<P class=MsoNormal style="MARGIN-BOTTOM: 6pt"><B><FONT face=Verdana color=#807f83 size=2><SPAN style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: #807f83; FONT-FAMILY: Verdana">E-mail: gregory.ryerson@savvis.net</SPAN></FONT></B></DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN style="FONT-SIZE: 12pt"> </SPAN></FONT></DIV></DIV><BR>This message contains information which may be confidential and/or privileged. Unless you are the intended recipient (or authorized to receive for the intended recipient), you may not read, use, copy or disclose to anyone the message or any information contained in the message. If you have received the message in error, please advise the sender by reply e-mail and delete the message and any attachment(s) thereto without retaining any copies.<BR></DIV><BR>-----Inline Attachment Follows-----<BR><BR>
<DIV class=plainMail>_______________________________________________<BR>Equest-users mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target=_blank>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</A><BR>To unsubscribe from this mailing list send a blank message to <A href="http://us.mc528.mail.yahoo.com/mc/compose?to=EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" ymailto="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR></DIV></BLOCKQUOTE></td></tr></table><br>