<div>Hello everyone, I'm a new eQuest user and working on my first LEED project. Fortunately and unfortunately, I am in charge of the energy modeling for the project. We are a two-man company and don't have many resources or other coworkers to turn to and figure things out collectively. Any help anyone can provide would be of much help. I've structured the questions to be specific and included background info and how I've implemented or believe I should implement input into eQuest. Other difficulties will be addressed in subsequent emails with similar structured questions. For your help I thank you in advance.</div>
<div> </div>
<div>The baseline model should have total fan power fixed based on total supply air volume. There's a section in Ashrae 90.1 G3.1.2.9 that says "Supply Fan Power. System fan electrical power for supply, return, exhaust, and relief shall be calculated using the following formulas:<br>
Pfan= 746 / ((1 - e^[-0.2437839 * ln(bhp) - 1.685541]) * bhp)<br>where,<br>Pfan = electric power to fan motor (watts)<br>bhp = brake hoursepower of baseline fan motor from Table G3.1.2.9, where cfm represents design supply flow rate." <br>
Table G3.1.2.9 has another formula for calculating baseline fan brake horsepower for buildings with less than 20000 cfm or more than 20000. Our building is under 20000 cfm so I would select the corresponding formula and obtain the bhp. I would then plug it in the formula above to obtain watts. What would I do with this? Would I take the fan power in watts and divide by our actual cfm for the building to obtain watts per cfm? Where should this be plugged into eQuest? So far I've found under Air-Side HVAC System Parameters and under Fans tab there's a text box next to Supply under Design kw/cfm with "n/a" as the value. If I restore the default of Static in WG, it allows the input of kw/cfm. Is this where I enter the calculated kw/cfm?<br>
Also fan mode must be set to continuous in the baseline and cycling in the proposed building. The wizard under HVAC equipment has options between continuous and intermittant but not sure about the detailed mode. Under Air-Side HVAC System Parameters and under Fans tab there's a pull down scroll labeled <span class="yshortcuts" id="lw_1246476468_10">fan control</span>. Then there's also night cycling. Are these two related? Not sure where to specify for continuous or cycling.<br>
</div>
<div>Thanks again,</div>
<div>Vince</div>