<div>Hello everyone, I'm a new eQuest user and working on my first LEED project. Fortunately and unfortunately, I am in charge of the energy modeling for the project. We are a two-man company and don't have many resources or other coworkers to turn to and figure things out collectively. Any help anyone can provide would be of much help. I've structured the questions to be specific and included background info and how I've implemented or believe I should implement input into eQuest. Other difficulties will be addressed in subsequent emails with similar structured questions. For your help I thank you in advance.</div>
<div> </div>
<div>Economizer has to be set for baseline building, which is easily accomplished thru the wizard but I'm not certain if it's necessary for anything to be done in the detailed mode regarding economizer or is the wizard sufficient? We're not going with economizer for proposed building. What kind of economizer should be used for baseline then? So far I figured drybulb temperature with a high-limit shut off of 75 deg for Zone 5b. Is this correct?<br>
 </div>
<div>Thanks again,</div>
<div>Vince</div>