<div>Please see numbered list further down to skip to issues or read background info below.</div>
<div> </div>
<div>We are using eQuest to model a storage facility and stand-alone retail office building for the storage. We have to follow LEED v2.2 requirements which calls upon Ashrae 90.1-2004 that specifically dictates the requirements for the baseline and proposed models. We are having problems entering and incorporating some of these requirements into eQuest and it's critical that we find a way to account for these requirements in order for us to achieve LEED EAc1 credit. The buildings have been modeled and we have preliminary results using EEM run measures that do not include certain requirements, which would most likely have to be modeled and run using parametric runs. If some of the requirements require to be modeled in the detailed mode then the entire simulation must be done using paramtric runs, which adds complexity as compared to the easy to run EEM measures using the wizard. I am still in the process of learning parametric runs. Any help provided would be much appreciated.</div>

<div> </div>
<div>1. The LEED reference guide requires that baseline model be sized using default ratios. I assume it refers to oversizing the HVAC cooling capacity by 15% and heating by 25% according to "G3.1.2.2 Equipment Capacities" but I am not sure where this information must be entered or specified. I suspect it must be entered in the detailed mode and simulated using parametric runs.</div>

<div> </div>
<div>2. The baseline model should have total fan power fixed based on total supply air volume. There's a section in Ashrae 90.1 G3.1.2.9 that says "Supply Fan Power. System fan electrical power for supply, return, exhaust, and relief shall be calculated using the following formulas:</div>

<div>Pfan= 746 / ((1 - e^[-0.2437839 * ln(bhp) - 1.685541]) * bhp)</div>
<div>where,</div>
<div>Pfan = electric power to fan motor (watts)</div>
<div>bhp = brake hoursepower of baseline fan motor from Table G3.1.2.9, where cfm represents design supply flow rate."</div>
<div> </div>
<div>Table G3.1.2.9 has another formula for calculating baseline fan brake horsepower for buildings with less than 20000 cfm or more than 20000. Our building is under 20000 cfm so we select the corresponding formula and obtain the bhp. I would then plug it in the formula above to obtain watts. What would I do with this? Would I take the fan power in watts and divide by our actual cfm for the building to obtain watts per cfm? Where should this be plugged into eQuest? Any ideas? Also fan mode must be set to continuous in the baseline and cycling in the proposed building and entered somewhere in the detailed mode if parametric runs have to be used.</div>

<div> </div>
<div>3. Economizer has to be set for baseline building, which is easily accomplished thru the wizard but not certain about where in the detailed mode for parametric runs. What kind of economizer should be used for baseline? Options in the wizard include drybulb temperature, enthalpy and dual enthalpy.</div>

<div> </div>
<div>4. Other smaller concerns include roof reflectivity must be 0.3 for baseline and 0.55 for proposed building which cannot be specified thru the wizard, only selected from available roof colors, none of which corresponding to those exact numbers. I would have to enter them in the detailed mode for parametric runs.</div>

<div> </div>
<div>Items 1 & 2 are of more concern since I don't know how to resolve them at this point. I have some ideas about items 3 & 4, just haven't had a chance to try them yet. Please let me know if you have any ideas or knowledge about eQuest and energy modeling for LEED EAc1 certification requirements. In the meantime I will continue to figure this out.</div>

<div> </div>
<div>Thanks to everyone</div>