<DIV dir=ltr align=left><SPAN class=558513513-17062009><FONT color=#0000ff
size=2 face=Arial>Hi Kimberley,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=558513513-17062009><FONT color=#0000ff
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=558513513-17062009><FONT color=#0000ff
size=2 face=Arial>I have recently dealt with this exact same problem. You need
to move the dummy zone system and zones in the .inp file you attached to the top
of the HVAC systems/zones list.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=558513513-17062009><FONT color=#0000ff
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=558513513-17062009><FONT color=#0000ff
size=2 face=Arial>Hope this helps.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=558513513-17062009><FONT color=#0000ff
size=2 face=Arial><BR>Dan.</FONT></SPAN></DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> equest-users-bounces@lists.onebuilding.org
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Kimberly
Killian<BR><B>Sent:</B> 17 June 2009 14:29<BR><B>To:</B>
equest-users@lists.onebuilding.org<BR><B>Subject:</B> [Equest-users] (no
subject)<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><FONT size=2 face=Verdana>
<DIV>Good afternoon,</DIV>
<DIV> </DIV>
<DIV>I am trying to add a mixed air unit onto a four-pipe fan coil system
through the use of a dummy zone, from which my real zones will get their outside
air. I get the following error:</DIV>
<DIV> </DIV>
<DIV>"EL1 Sys1 (FC) (G.E16) defined before its OA-FROM-SYSTEM. This will cause
incorrect OA temperature calculation. Move this SYSTEM to be defined before its
OA-FROM-SYSTEM in the project BDL input file."</DIV>
<DIV> </DIV>
<DIV>The catch is that there is no BDL file, as the simulation aborts before it
is complete. Is there another way to define the MAU before the Fan Coil System.
I have searched a number of terms in the user's group and there are many
questions related to this topic, but I can't find any answers. Any help would be
appreciated.</DIV>
<DIV> </DIV>
<DIV>Regards,</DIV>
<DIV>Kimberly Killian<BR>Northern Architects, Inc.<BR>207 King Street Suite
3<BR>Burlington VT 05401<BR>T: 802-658-1953<BR>F:
802-658-2975</DIV></FONT></DIV><BR>______________________________________________________________________<BR>This
email has been scanned by the MessageLabs Email Security System.<BR>For more
information please visit http://www.messagelabs.com/email
<BR>______________________________________________________________________<BR>
<BR>
______________________________________________________________________<BR>
This email has been scanned by the MessageLabs Email Security System.<BR>
For more information please visit http://www.messagelabs.com/email <BR>
______________________________________________________________________<BR>
</BODY></HTML>