<DIV><SPAN class=189424018-15062009><FONT face=Arial size=2>I'm modeling a 
single story building with 2 packaged rooftop HP units in Las Vegas. I have 
allowed the program to autosize airflow and cooling and heating 
capacities.</FONT></SPAN></DIV>
<DIV><SPAN class=189424018-15062009><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=189424018-15062009><FONT face=Arial size=2>I'm guessing that 
the high amount of underheated hours is due to the fact that the PSZ system 
type uses only one of its assigned zones as the control for constant volume 
airflow.  I have designated the control zone as the zone with the 
highest internal loads.  This works OK in cooling mode, though, I 
still have about 400 undercooled hours.  But in heating mode, the zone 
with the highest internal loads does not need as much heat as the other 
zones.  Since it's a constant volume system and the control zone is saying 
"no heat needed", the rest of the zones are not getting any heat.  Is that 
right??</FONT></SPAN></DIV>
<DIV><SPAN class=189424018-15062009><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=189424018-15062009><FONT face=Arial size=2>Following through 
with the assumption above, I tried to increase the minimum cfm/sqft on zone 
level to 0.5, but my underheated hours went up.</FONT></SPAN></DIV>
<DIV><SPAN class=189424018-15062009><FONT face=Arial size=2>I only manage 
to decrease unmet heating hours after I increase 
the cfm on the system level to about 5 times what Trane 
sizes. </FONT></SPAN></DIV>
<DIV><SPAN class=189424018-15062009><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=189424018-15062009><FONT face=Arial size=2>Can someone help me 
out here?</FONT></SPAN></DIV>
<DIV><SPAN class=189424018-15062009><FONT face=Arial size=2>Thank 
you!!</FONT></SPAN></DIV>
<DIV><SPAN class=189424018-15062009><FONT face=Arial 
size=2>Linda</FONT></SPAN></DIV>
<DIV><SPAN class=189424018-15062009><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV align=left><IMG 
alt="
Linda Lam, LEED® AP
WSP Flack + Kurtz
405 Howard Street, Suite 500
San Francisco, CA 94105
Direct: 415.402.5813
Main Tel: 415.398.3833
Fax: 415.433.5311
website: http://www.wspfk.com
vCard: http://vcards.wspfk.com/vcardloader.php?filename=flackkurtz-linda-lam-wspfk-com-1227040073.vcf
image: " 
src="http://vcards.wspfk.com/usercard.php?filename=flackkurtz-linda-lam-wspfk-com-1227040073.png" 
align=absMiddle useMap=#flackkurtz-linda-lam-wspfk-com-1227040073 border=0 
nosend="1">  
<STYLE>
a {color: 1D88F6;}
</STYLE>
<MAP name=flackkurtz-linda-lam-wspfk-com-1227040073><AREA shape=RECT 
  target=_blank coords=401,9,458,31 href="http://www.wspfk.com"><AREA shape=RECT 
  target=_blank coords=458,9,503,31 
  href="http://vcards.wspfk.com/vcardloader.php?filename=flackkurtz-linda-lam-wspfk-com-1227040073.vcf"><AREA 
  shape=RECT target=_blank coords=503,9,536,31 
  href="http://maps.google.com/maps?f=q&hl=en&geocode=&q=405+Howard+Street,+San+Francisco,+CA+94105&sll=40.754409,-73.988972&sspn=0.019083,0.032616&ie=UTF8&ll=37.79032,-122.395163&spn=0.019908,0.032616&z=15&iwloc=addr"><AREA 
  shape=RECT target=_blank coords=536,9,578,31 
  href="mailto:linda.lam@wspfk.com"><AREA shape=RECT target=_blank 
  coords=0,31,591,161 href="http://www.wspfk.com"></MAP></DIV>
<DIV> </DIV></BODY></HTML>