If the objective is to be able to create binary (.bin) weather files
for use in DOE-2, then you definitely need to use the weather file
converter mentioned (or some other custom utility). One thing I seem
to recall about this mechanism is that it is very column sensitive -
meaning the data needs to be lined up properly in fields of a certain
length in order for the text format to get read into the converter in
creating a binary.<br>
<br>
If however your objective is simply to be able to see or graph the
weather data contained in the DOE-2 binary weather file, then you can
do this much more easily via eQUEST. Starting with a building model
that references the desired weather file (in the detailed edit mode),
create an hourly report that references the desired weather data
variables (report block type = GLOBAL provides access to most, if not
all?, of the weather data streams). Simulate the model, and once
completed, select File - Export Hourly Results... This will generate
(and open) a CSV file with the specified weather data streams.<br>
<br>
- Scott<br>
<br>
<br>
Matthew Higgins wrote:
<blockquote cite="mid:4A15956B.3020209@edi-arch.com" type="cite">I've
been trying to resolve this as well and haven't received any insight.
Attached is my workflow... maybe you'll see my error.
<br>
<br>
Matthew Higgins, LEED AP + ASHRAE-HBDP
<br>
Building Performance Specialist
<br>
Environmental Dynamics, Inc.
<br>
Architecture and Sustainability Consulting Services
<br>
505.242.2851 xt.103
<br>
<br>
Any data provided by the Consultant, verbal or written, are to be
considered opinions of building energy and/or daylight performance. The
Client understands that the Consultant has no control of occupant
habits, equipment or material performance or characteristics, site or
climate conditions or the Contractor's method of assembly, and that the
Consultant's opinions regarding building energy/daylight performance
are made on the basis of the Consultant's professional judgment and
experience. The Consultant makes no warranty, express or implied, that
the energy/daylight performance of the building will not vary from the
Consultant's opinion of building energy/daylight performance.
<br>
<br>
Anthony Hardman wrote:
<br>
<br>
<blockquote type="cite">Can anyone provide /step by step/
instructions on how to convert bin files to text files using the DOEWth
converter? I still can’t figure it out after reading the few
suggestions in the archives. Why isn’t there a manual for this sort of
thing? I don’t speak DOS or Binary so the “readme” file isn’t much
help. Thanks.
<br>
<br>
*Anthony Hardman*
<br>
<br>
Mechancial Engineer
<br>
<br>
LEED AP
<br>
<br>
Geo-Energy Services
<br>
<br>
14250 E Easter Pl, STE C
<br>
<br>
Centennial, CO 80112
<br>
<br>
303-531-5292 v
<br>
<br>
303-805-3563 f
<br>
<br>
720-273-9973 c
<br>
<br>
_www.GeoEnergyServices.com <a class="moz-txt-link-rfc2396E" href="http://www.geoenergyservices.com"><http://www.geoenergyservices.com></a>_
<br>
<br>
------------------------------------------------------------------------
<br>
<br>
_______________________________________________
<br>
Equest-users mailing list
<br>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
<br>
To unsubscribe from this mailing list send a blank message to
<a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
<br>
<br>
<br>
</blockquote>
<br>
<pre wrap="">
<hr size="4" width="90%">
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>