<br><font size=2 face="sans-serif">Jason,</font>
<br>
<br><font size=2 face="sans-serif">There is a bug in V3.63 that defaults
zone heating minimum flow ratio to 1.00 (technically, I think it defaults
to the system minimum overall supply ratio), rather than the system heating
minimum flow ratio (which defaults to 0.01).  This will cause systems
with variable heating air flow to use a lot more fan and heating energy
than expected.</font>
<br>
<br><font size=2 face="sans-serif">You can either change all of your zone
flows manually or set a user-defined default code snippet: for the zone
heating minimum air flow (or insert this bit of code in your .inp file).</font>
<br>
<br><font size=2 face="sans-serif">if (#P("HMIN-CFM-RATIO") ==
unused)</font>
<br><font size=2 face="sans-serif">    then unused</font>
<br><font size=2 face="sans-serif">    else if (#RV(#P("HMIN-CFM-RATIO"))
== 0)</font>
<br><font size=2 face="sans-serif">          then
#P("HMIN-CFM-RATIO")</font>
<br><font size=2 face="sans-serif">          else
no_default</font>
<br><font size=2 face="sans-serif">         endif</font>
<br><font size=2 face="sans-serif">   endif</font>
<br>
<br>
<br><font size=2 face="sans-serif">Hope this helps,</font>
<br><font size=2 face="sans-serif">Clayton</font>
<br>
<p><font size=3 face="Times New Roman"> </font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td width=40%><font size=1 face="sans-serif"><b>Charles Land <cland@geo-marine.com></b>
</font>
<br><font size=1 face="sans-serif">Sent by: equest-users-bounces@lists.onebuilding.org</font>
<p><font size=1 face="sans-serif">05/21/2009 11:08 AM</font>
<td width=59%>
<table width=100%>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">To</font></div>
<td><font size=1 face="sans-serif">"equest-users@lists.onebuilding.org"
<equest-users@lists.onebuilding.org></font>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">cc</font></div>
<td>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">Subject</font></div>
<td><font size=1 face="sans-serif">[Equest-users] new equest</font></table>
<br>
<table>
<tr valign=top>
<td>
<td></table>
<br></table>
<br>
<br>
<br><font size=2 face="Calibri">Has anyone ran any of their old files in
the new equest yet.  My numbers have significantly changed.  I
am working on ECMs and my constant volume alternative is saving more money
than my vav alternative.  Is anyone else having any problems with
this.  Should I not be running 3.61 file on 3.63?</font>
<br><font size=2 face="Calibri"> </font>
<br><font size=2 color=#1f497d>Charles (Jason) Land</font>
<br><font size=2 color=#1f497d>Project Engineer</font>
<br><font size=2 color=#1f497d>Geo-Marine, Inc | Energy Services Group</font>
<br><font size=2 color=#1f497d>146 Market Place Boulevard | Knoxville,
TN  37922</font>
<br><font size=2 color=#1f497d>Office: (865) 692-0084 | Fax: (865) 692-0560</font>
<br><font size=2 face="Calibri"> </font><font size=2><tt>_______________________________________________<br>
Equest-users mailing list<br>
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<br>
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<br>
</tt></font>
<br>