<br><font size=2 face="sans-serif">Jason,</font>
<br>
<br><font size=2 face="sans-serif">There is a bug in V3.63 that defaults
zone heating minimum flow ratio to 1.00 (technically, I think it defaults
to the system minimum overall supply ratio), rather than the system heating
minimum flow ratio (which defaults to 0.01). &nbsp;This will cause systems
with variable heating air flow to use a lot more fan and heating energy
than expected.</font>
<br>
<br><font size=2 face="sans-serif">You can either change all of your zone
flows manually or set a user-defined default code snippet: for the zone
heating minimum air flow (or insert this bit of code in your .inp file).</font>
<br>
<br><font size=2 face="sans-serif">if (#P(&quot;HMIN-CFM-RATIO&quot;) ==
unused)</font>
<br><font size=2 face="sans-serif">&nbsp; &nbsp; then unused</font>
<br><font size=2 face="sans-serif">&nbsp; &nbsp; else if (#RV(#P(&quot;HMIN-CFM-RATIO&quot;))
== 0)</font>
<br><font size=2 face="sans-serif">&nbsp; &nbsp; &nbsp; &nbsp; &nbsp; then
#P(&quot;HMIN-CFM-RATIO&quot;)</font>
<br><font size=2 face="sans-serif">&nbsp; &nbsp; &nbsp; &nbsp; &nbsp; else
no_default</font>
<br><font size=2 face="sans-serif">&nbsp; &nbsp; &nbsp; &nbsp; &nbsp;endif</font>
<br><font size=2 face="sans-serif">&nbsp; &nbsp;endif</font>
<br>
<br>
<br><font size=2 face="sans-serif">Hope this helps,</font>
<br><font size=2 face="sans-serif">Clayton</font>
<br>
<p><font size=3 face="Times New Roman">&nbsp;</font>
<br>
<br>
<br>
<table width=100%>
<tr valign=top>
<td width=40%><font size=1 face="sans-serif"><b>Charles Land &lt;cland@geo-marine.com&gt;</b>
</font>
<br><font size=1 face="sans-serif">Sent by: equest-users-bounces@lists.onebuilding.org</font>
<p><font size=1 face="sans-serif">05/21/2009 11:08 AM</font>
<td width=59%>
<table width=100%>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">To</font></div>
<td><font size=1 face="sans-serif">&quot;equest-users@lists.onebuilding.org&quot;
&lt;equest-users@lists.onebuilding.org&gt;</font>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">cc</font></div>
<td>
<tr valign=top>
<td>
<div align=right><font size=1 face="sans-serif">Subject</font></div>
<td><font size=1 face="sans-serif">[Equest-users] new equest</font></table>
<br>
<table>
<tr valign=top>
<td>
<td></table>
<br></table>
<br>
<br>
<br><font size=2 face="Calibri">Has anyone ran any of their old files in
the new equest yet. &nbsp;My numbers have significantly changed. &nbsp;I
am working on ECMs and my constant volume alternative is saving more money
than my vav alternative. &nbsp;Is anyone else having any problems with
this. &nbsp;Should I not be running 3.61 file on 3.63?</font>
<br><font size=2 face="Calibri">&nbsp;</font>
<br><font size=2 color=#1f497d>Charles (Jason) Land</font>
<br><font size=2 color=#1f497d>Project Engineer</font>
<br><font size=2 color=#1f497d>Geo-Marine, Inc | Energy Services Group</font>
<br><font size=2 color=#1f497d>146 Market Place Boulevard | Knoxville,
TN &nbsp;37922</font>
<br><font size=2 color=#1f497d>Office: (865) 692-0084 | Fax: (865) 692-0560</font>
<br><font size=2 face="Calibri">&nbsp;</font><font size=2><tt>_______________________________________________<br>
Equest-users mailing list<br>
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<br>
To unsubscribe from this mailing list send &nbsp;a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<br>
</tt></font>
<br>