I&#39;m just finishing up the LEED energy modeling for a manufacturing plant where the unregulated process loads (compressed air, manufacturing tools, producing de-ionized water, etc.) is 76% of the total energy cost. We&#39;re able to achieve the required 10% savings over 90.1-2007 (for LEED 2009) with an extremely efficient chiller plant, aggressive daylighting and lighting controls,  heat recovery, and on site PV. We&#39;re submitting an exceptional calculation method for process load savings because we&#39;ve recovered enough heat from the compressed air to completely eliminate the need for the process heating, and used more efficient tools. If the ECM gets accepted, we could get 3 more energy points, but we&#39;re planning on having to meet the required 10% without any ECMs.<br>
<br>One interesting thing that I discovered - ASHRAE 90.1-2007 is a bit more forgiving on manufacturing facilitieis because of the revised fan power calcs that let you take additional static pressure allowances for many things. If you&#39;re under LEED 2.2 and want to use 90.1-2004, I would strongly recommmend at least using the addenda that picks up this fan power change.<br>
<br><br>-- <br>Kendra Tupper<br>Senior Consultant<br>Built Environment Team<br><br>Rocky Mountain Institute  |  T  303-567-8641 |  F  303-245-7213  |  <a href="http://www.rmi.org">www.rmi.org</a><br><br><div class="gmail_quote">
On Thu, May 21, 2009 at 7:33 AM, Ramana Koti <span dir="ltr">&lt;<a href="mailto:ramana.koti@gmail.com">ramana.koti@gmail.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
<div bgcolor="#FFFFFF"><div>If you look up Credit Interpretation Requests on EA Cr1, you&#39;ll see that an alternate compliance path can be proposed that&#39;s specific to your  manufacturing facility, especially for end uses not regulated by Ashrae 90.1. </div>
<div><br></div><div>You&#39;d probably still have to include all end uses.</div><div><br></div><font color="#888888"><div>Ramana.  <br><br><br></div></font><div class="im"><div><br>On May 21, 2009, at 4:39 AM, <a href="mailto:cic@jci.com" target="_blank">cic@jci.com</a> wrote:<br>
<br></div><div></div></div><div><div></div><div class="h5"><blockquote type="cite"><div>
<br><font size="2" face="sans-serif">Dear All,</font>
<br>
<br><font size="2" face="sans-serif">Refer the following data. </font>
<br>
<br><font size="2" face="sans-serif">A  manufacturing building has the
following area</font>
<br>
<br><font size="2" face="sans-serif">Common area,office area    
                     
                     
           = 22% of the building area which
contribute 13% of a/c requirement</font>
<br><font size="2" face="sans-serif">Manufacturing area   (clean room++)
                     
                = 57% of the building
area which contribute 87% of a/c requirement</font>
<br><font size="2" face="sans-serif">Un air-conditioned area    
                     
                     
                = 21% of the building
area.</font>
<br>
<br><font size="2" face="sans-serif">Now this building needs LEED Certification.
</font>
<br>
<br><font size="2" face="sans-serif"> To achieve EA Credit1, whether
the clean room load(process)  needs to be considered in baseline design
during modelling? or only we need to consider the common area+office area+Unconditioned
area.</font>
<br>
<br><font size="2" face="sans-serif">Advance thanks for your valuable feedback.</font>
<br>
<br><font size="2" face="sans-serif">Thanks and regards</font>
<br><font size="2" face="sans-serif">Kathiresan</font>
<br>
<br>
<br></div></blockquote></div></div><div class="im"><blockquote type="cite"><div><span>_______________________________________________</span><br><span>Equest-users mailing list</span><br><span><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a></span><br>
<span>To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank"></a><a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span><br>
</div></blockquote></div></div><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>