<FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'>The values in the Loads reports represent the end use contribution of cooling <I>loads</I>, not energy consumed to meet those cooling loads. The BEPS and BEPU reports show end use <I><U>energy</U></I> consumption and include the effects of equipment efficiency, etc.<BR>
<BR>
As Vikram pointed out, the Loads reports do not include ventilation loads, which is a significant portion of the cooling loads – has anyone ever figured out a way to get the load breakdown including the OA contribution? Perhaps from custom hourly reports?<BR>
<BR>
<BR>
On 1/8/09 10:03 AM, "Lam, Linda" <<a href="linda.lam@wspfk.com">linda.lam@wspfk.com</a>> wrote:<BR>
<BR>
</SPAN></FONT><BLOCKQUOTE><SPAN STYLE='font-size:11pt'><FONT COLOR="#0000FF"><FONT FACE="Arial">Vikram,<BR>
</FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
</FONT><FONT COLOR="#0000FF"><FONT FACE="Arial">The total MBTU used for cooling from the LS-F report does is much greater than the space cooling enduse value in the BEPS report. Does the total MBTU in LSF represent all energy including (heat rejection, pumps and ventilation fans) associated with cooling the building? Thanks for your help!<BR>
</FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
</FONT><FONT COLOR="#0000FF"><FONT FACE="Arial">LS-F Report:<BR>
<IMG src="cid:3314254077_1604621" ><BR>
</FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"> <BR>
</FONT><FONT COLOR="#0000FF"><FONT FACE="Arial">BEPS report:<BR>
</FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><IMG src="cid:3314254077_1626146" ><BR>
<BR>
<BR>
<BR>
<HR ALIGN=CENTER SIZE="3" WIDTH="100%"></FONT><FONT FACE="Tahoma, Verdana, Helvetica, Arial"><B>From:</B> Vikram Sami [<a href="mailto:VSami@lasarchitect.com">mailto:VSami@lasarchitect.com</a>] <BR>
<B>Sent:</B> Thursday, January 08, 2009 8:49 AM<BR>
<B>To:</B> Lam, Linda; <a href="equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><BR>
<B>Subject:</B> RE: NINJA-SPAM:[Equest-users] Which report tells me how Space Cooling is divided up?<BR>
</FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><BR>
<FONT COLOR="#0025C4">Linda,<BR>
<BR>
LS-F gives you the building monthly load components for cooling and heating. <BR>
LS-C gives you the building peak load components. <BR>
<BR>
LS-E & LS-B give you the space loads <BR>
<BR>
NOTE: These reports do not include the ventilation loads ˆ I think those are added at the system level. <BR>
</FONT><BR>
</FONT></SPAN><FONT FACE="Garamond"><SPAN STYLE='font-size:12pt'><B>Vikram Sami,</B></SPAN></FONT><SPAN STYLE='font-size:12pt'><FONT COLOR="#0025C4"><FONT FACE="Times New Roman"> </FONT></FONT><FONT FACE="Garamond">LEED AP</FONT><FONT COLOR="#0025C4"><FONT FACE="Times New Roman"> <BR>
</FONT></FONT><FONT FACE="Garamond">Direct Phone 404-253-1466 | Direct Fax 404-253-1366</FONT><FONT COLOR="#0025C4"><FONT FACE="Times New Roman"> <BR>
</FONT></FONT><FONT COLOR="#800000"><FONT FACE="Garamond"><B>L</B></FONT></FONT></SPAN><FONT COLOR="#800000"><FONT FACE="Garamond"><B><FONT SIZE="2"><SPAN STYLE='font-size:10pt'>ORD</SPAN></FONT><SPAN STYLE='font-size:12pt'>, A</SPAN><FONT SIZE="2"><SPAN STYLE='font-size:10pt'>ECK</SPAN></FONT><SPAN STYLE='font-size:12pt'> & S</SPAN><FONT SIZE="2"><SPAN STYLE='font-size:10pt'>ARGENT</SPAN></FONT><SPAN STYLE='font-size:12pt'> A</SPAN><FONT SIZE="2"><SPAN STYLE='font-size:10pt'>RCHITECTURE<BR>
</SPAN></FONT></B></FONT></FONT><FONT FACE="Garamond"><FONT SIZE="2"><SPAN STYLE='font-size:10pt'><FONT COLOR="#0025C4">1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361</FONT></SPAN></FONT></FONT><FONT COLOR="#0025C4"><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Garamond"><SPAN STYLE='font-size:10pt'>Responsive Design</SPAN></FONT></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> </SPAN></FONT><FONT SIZE="1"><FONT FACE="Symbol"><SPAN STYLE='font-size:7pt'>·</SPAN></FONT></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> </SPAN></FONT><FONT SIZE="2"><FONT FACE="Garamond"><SPAN STYLE='font-size:10pt'>Technological Expertise</SPAN></FONT></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> </SPAN></FONT><FONT SIZE="1"><FONT FACE="Symbol"><SPAN STYLE='font-size:7pt'>·</SPAN></FONT></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> </SPAN></FONT><FONT SIZE="2"><FONT FACE="Garamond"><SPAN STYLE='font-size:10pt'>Exceptional Service</SPAN></FONT></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT></FONT><FONT COLOR="#007F00"><FONT SIZE="2"><FONT FACE="Garamond"><SPAN STYLE='font-size:10pt'>Please visit our new website</SPAN></FONT></FONT></FONT><FONT COLOR="#0025C4"><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> </SPAN></FONT></FONT><SPAN STYLE='font-size:12pt'><FONT FACE="Garamond">|</FONT><FONT COLOR="#0025C4"><FONT FACE="Times New Roman"> </FONT></FONT></SPAN><FONT COLOR="#0000FF"><FONT SIZE="2"><FONT FACE="Garamond"><SPAN STYLE='font-size:10pt'>www.lordaecksargent.com</SPAN></FONT></FONT></FONT><FONT COLOR="#0025C4"><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <<a href="file:///\\www.lordaecksargent.com\">file:///\\www.lordaecksargent.com\</a>> <BR>
</SPAN></FONT></FONT><FONT COLOR="#007F00"><FONT SIZE="6"><FONT FACE="Webdings"><SPAN STYLE='font-size:24pt'>P </SPAN></FONT></FONT><FONT SIZE="2"><FONT FACE="Garamond"><SPAN STYLE='font-size:10pt'>Think GREEN before you print.<BR>
</SPAN></FONT></FONT></FONT><FONT COLOR="#0025C4"><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'> <BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Tahoma, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:10pt'><B>From:</B> <a href="equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a> [<a href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>] <B>On Behalf Of </B>Lam, Linda<BR>
<B>Sent:</B> Thursday, January 08, 2009 11:42 AM<BR>
<B>To:</B> <a href="equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><BR>
<B>Subject:</B> NINJA-SPAM:[Equest-users] Which report tells me how Space Cooling is divided up?<BR>
</SPAN></FONT></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>Dear eQuest Users<BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>Does anyone know which report will tell me how Space Cooling is divided up? ie, cooling energy attributed to envelope loads, lighting loads and equipment loads.<BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT SIZE="2"><FONT FACE="Arial"><SPAN STYLE='font-size:10pt'>Thanks!<BR>
</SPAN></FONT></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
<IMG src="cid:3314254077_1571583" > <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
</SPAN></FONT><FONT FACE="Times New Roman"><SPAN STYLE='font-size:12pt'> <BR>
</SPAN></FONT><FONT FACE="Calibri, Verdana, Helvetica, Arial"><SPAN STYLE='font-size:11pt'><BR>
<HR ALIGN=CENTER SIZE="3" WIDTH="95%"></SPAN></FONT><FONT SIZE="2"><FONT FACE="Consolas, Courier New, Courier"><SPAN STYLE='font-size:10pt'>_______________________________________________<BR>
Equest-users mailing list<BR>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><BR>
To unsubscribe from this mailing list send a blank message to <a href="EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><BR>
</SPAN></FONT></FONT></BLOCKQUOTE>
</BODY>
</HTML>