If you have a cooling design day specified, but no heating design day specified, then the design day report will only give you cooling design, and not heating design.  The program default design days should include both.<br>
<br>--<br>Karen<br><br><div class="gmail_quote">On Thu, Dec 4, 2008 at 11:51 AM,  <span dir="ltr"><<a href="mailto:Gary.Schrader@tac.com">Gary.Schrader@tac.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">






<div vlink="purple" link="blue" lang="EN-US">
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span>Brian,</span></font></div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span></span></font> </div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span>You have a significant amount of light and occupant 
load in your building. Are you using a heating design day? Does that design day 
call for a heating design day schedule? Does that heating design day schedule 
shut down the lights/occupants during the course of the day such that no 
light/occupant load is contributed to the space during the heating 
season?</span></font></div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span></span></font> </div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span>My prediction is that your lights/occupants/etc. are 
still scheduled during the winter months and thus your building doesn't NEED 
heat. Check your schedules to ensure that the above items are "off" during the 
winter months such that the room isn't heating itself.</span></font></div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span></span></font> </div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span>Another way to prove this would be to run an hourly 
report and check to see if your cooling coil(s) is/are in use during all days of 
the year.</span></font></div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span></span></font> </div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span>Just an idea of where to start.</span></font></div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span></span></font> </div>
<div dir="ltr" align="left"><font size="2" color="#0000ff" face="Verdana"><span>Thanks,</span></font><font style="font-family: Verdana; font-style: normal; font-variant: normal; font-weight: normal; font-size: 8pt; line-height: normal; font-size-adjust: none; font-stretch: normal;" face="verdana"><br>
<b>Gary Schrader<br></b>Engineer I<br><br><b>TAC<br></b>16011 
College Blvd, Suite 212<br>Lenexa, KS  66219<br><br>
<table style="font-family: verdana; font-style: normal; font-variant: normal; font-weight: normal; font-size: 8pt; line-height: normal; font-size-adjust: none; font-stretch: normal;" cellpadding="0" cellspacing="0">
  <tbody>
  <tr>
    <td>Direct:</td>
    <td>+1 </td></tr>
  <tr>
    <td>Fax:</td>
    <td>+1 913-469-0206</td></tr>
  <tr>
    <td>Mobile:</td>
    <td>+1 913-217-8068</td></tr>
  <tr>
    <td>Email:</td>
    <td><a href="mailto:Gary.Schrader@tac.com" target="_blank">Gary.Schrader@tac.com</a></td></tr>
  <tr>
    <td>Web:</td>
    <td><a href="http://www.tac.com/" target="_blank">www.tac.com</a></td></tr></tbody></table><br>Notice: 
This email message, together with any attachments, contains information of TAC, 
which may be confidential, proprietary, copyrighted and/or legally privileged. 
This email is intended solely for the use of the individual or entity named on 
the message. If you are not the intended recipient, and have received this 
message in error, please immediately return by email and then delete it. </font></div>
<div></div>
<div> </div><br>
<div dir="ltr" align="left" lang="en-us">
<hr>
<font size="2" face="Tahoma"><b>From:</b> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> 
[mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Brian 
Davis<br><b>Sent:</b> Thursday, December 04, 2008 10:44 AM<br><b>To:</b> 
<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> [Equest-users] eQUEST 
building skin effects in cooling but notheating<br></font><br></div><div><div></div><div class="Wj3C7c">
<div></div>
<div>
<p>I am using the refrigeration version of equest 3.61 and have 
several zones within the building which have exterior walls and roof.  The 
equest output notes loads in cooling for them but not in heating while other 
zones properly indicate loads for both cooling and heating, has anyone else run 
across this and can suggest something for me to check.  The output is 
listed below.</p>
<p> </p>
<p> </p>
<p> </p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">REPORT- 
LS-B Space Peak Load Components     EL1 NNE Perim Spc 
(G.NNE16)                     
WEATHER FILE- Baltimore    MD TMY2</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">---------------------------------------------------------------------------------------------------------------------------------</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">SPACE  EL1 NNE Perim Spc 
(G.NNE16)     </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">SPACE 
TEMPERATURE USED FOR THE LOADS CALCULATION IS   70 F /  21 
C</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">                    
MULTIPLIER        
1.0          FLOOR 
MULTIPLIER        1.0</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">                    
FLOOR  AREA     28544  
SQFT      2652   M2 </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">                    
VOLUME         513785  
CUFT     14550   M3 </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">                                          
COOLING  
LOAD                               
HEATING  LOAD</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">                                     
==========================                
==========================</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">    
TIME                                    
AUG  3  
7PM                                             
</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">    DRY-BULB 
TEMP                      
93 F             34 
C</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">    WET-BULB 
TEMP                      
76 F             24 
C</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">    TOT 
HORIZONTAL SOLAR RAD           
80 BTU/H.SQFT   252 W/M2</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">    WINDSPEED 
AT 
SPACE                
5.3 KTS          2.7 
M/S</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">    CLOUD 
AMOUNT 
0(CLEAR)-10            
0</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">                                  
SENSIBLE            
LATENT                              
SENSIBLE     </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">                            
(KBTU/H)    ( KW )  (KBTU/H)  ( KW 
)                     
(KBTU/H)  ( KW )  </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">                            
--------    ------  --------  
------                     
--------  --------</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     WALL 
CONDUCTION           
4.394     1.287     0.000   
0.000                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     ROOF 
CONDUCTION          
28.204     8.264     0.000   
0.000                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
WINDOW GLASS+FRM COND     0.000     
0.000     0.000   
0.000                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
WINDOW GLASS SOLAR        
0.000     0.000     0.000   
0.000                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     DOOR 
CONDUCTION           
0.000     0.000     0.000   
0.000                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
INTERNAL SURFACE COND     0.000     
0.000     0.000   
0.000                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
UNDERGROUND SURF COND    -0.666    
-0.195     0.000   
0.000                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
OCCUPANTS TO SPACE       
18.451     5.406    15.444   
4.525                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
LIGHT     TO SPACE      
144.060    42.209     0.000   
0.000                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
EQUIPMENT TO SPACE        
0.000     0.000     0.000   
0.000                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
PROCESS   TO SPACE        
0.000     0.000     0.000   
0.000                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
INFILTRATION              
1.692     0.496     2.090   
0.612                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">                            
--------   -------   -------  
------                     
--------  --------</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
TOTAL                   
196.134    57.467    17.534   
5.137                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
TOTAL / 
AREA              
0.007     0.022     0.001   
0.002                        
0.000     0.000</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
TOTAL 
LOAD              
213.669 KBTU/H       62.605  
KW                  
0.000 KBTU/H        0.000  KW 
</span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';">     
TOTAL LOAD / AREA         7.49  
BTU/H.SQFT   23.609  
W/M2                
0.000 BTU/H.SQFT    0.000  W/M2 </span></p>
<p><span style="font-size: 8pt; font-family: 'Courier New';"> </span></p>
<p> </p></div></div></div></div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>