I'm not sure what others experience has been but:<div><br></div><div>1.  I believe the heat exchanger module is basically to attach a cooling tower to a loop, nothing else</div><div><br></div><div>2.  I have had trouble having eQuest properly recovery heat from a loop.  I have found that using chillers, eQuest will only recover up to 100% of the chiller's hourly capacity (chillers usually reject more than 100% to the CW loop), also, sometimes much less than 100% is recovered.</div>
<div><br></div><div>3.  With the loop-to-loop heat pump, I recall it being called on by a cooling load, and not by a heating load.  In other words, it will reject heat to a heating loop only when a cooling load exists, but will not turn on if only a heating load exists.  I'd be delighted if anyone can tell me how to operate it otherwise.</div>
<div><br></div><div>I recently completed a project that required modeling heat recovery.  I ended up using the hourly outputs, and calculating in an excel spreadsheet.  I did get some test models that appeared to work, but when I looked at the hourly results, sometimes only 15% of the heat was being recovered when the HW loop could've used 100% why... I don't know.</div>
<div><br></div><div>Hope this helps, and eQuest developers--I'd love to see a solution to the above issues.  I think that myself and some others on this list-serve would contribute to the cost of making improvements, if possible.</div>
<div><br></div><div>Thanks,</div><div><br></div><div>--</div><div>Karen Walkerman<br><br><div class="gmail_quote">On Wed, Dec 3, 2008 at 5:35 PM, Eric Youngson <span dir="ltr"><<a href="mailto:eyoungson@rmi.org">eyoungson@rmi.org</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">








<div lang="EN-US" link="blue" vlink="purple">

<div>

<p>equest-users,</p>

<p>                                I
am trying to connect two water loops in order to recover heat with a water to
water heat pump. I was trying to do this with a heat exchanger but the heat exchanger
module doesn't seem to be able to attach to a loop! I am a missing
something or is the heat exchanger not functional?</p>

<p> </p>

<p>Thx</p>

<p><span style="font-size:10.0pt"> </span></p>

<p><span style="font-family:"Garamond","serif""> </span></p>

<p><span style="font-family:"Garamond","serif"">Eric Allen
Youngson</span></p>

<p><span style="font-family:"Garamond","serif";color:gray">303.245.8586</span><span style="font-size:9.0pt;font-family:"Garamond","serif";color:gray"><br>
</span><span style="font-family:"Garamond","serif""><br>
</span><span style="font-size:14.0pt;font-family:"Garamond","serif"">Rocky
Mountain Institute  </span><span style="font-family:"Garamond","serif";color:gray"><br>
</span><span style="font-size:10.0pt;font-family:"Garamond","serif"">1820
Folsom Street Boulder, CO 50302</span><span style="font-family:"Garamond","serif""></span></p>

<p><span style="font-family:"Garamond","serif""><br>
</span><span style="font-size:10.0pt;font-family:"Garamond","serif"">Rocky
Mountain Institute fosters the efficient and restorative use of<br>
resources to make the world secure, just, prosperous, and life-sustaining.</span></p>

<p> </p>

</div>

</div>


<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>