Jon-<br><br>Let me know if this helps.<br><br>-You need to create a chiller of type "Loop-to-Loop Heat Pump". <br><br>-You will need to specify the CHW Loop, CW Loop, and HW Loop. <br><br>-However, the CW Loop is actually a "Lake/Well" type loop. <br>
<br>-The Lake/Well Loop needs to have a Lake/Well GLHX attached to it.<br><br>-I would also reccomend installing a top up boiler to the hw loop.<br><br>This way you have a geothermal chiller that is connected to a ground well. This chiller is producing both hot and cold water that can be connected to any type of air-side system you wish.<br>
<br>Hope that was what you were looking for,<br><br>-- <br>Steve Mignogna<br>Atelier Ten<br><br><br><br><div class="gmail_quote">On Wed, Nov 26, 2008 at 8:59 AM, Jon Evans <span dir="ltr"><<a href="mailto:jevans@sustaineng.com">jevans@sustaineng.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">I have a unique system I'm trying to setup in Equest and was wondering if it<br>
is possible, and if so, what the trick is.<br>
<br>
I would like to couple a VAV system to water-to-water geothermal heat pumps.<br>
So essentially I will have a VAV system on the terminal side and the heating<br>
and cooling plants will be geothermal water-to-water heat pumps. One will<br>
feed the chilled water coil in the air handler, and another the reheat coils<br>
at the VAV boxes.<br>
<br>
I can set up a heat pump chiller that feeds the air handler with a<br>
geothermal condensing loop. But I'm having problems attaching a heat pump<br>
to the hot water loop, and the hot water loop to the geothermal condensing<br>
loop.<br>
<br>
Thanks for any insight you might have. Hope everyone has a nice holiday!<br>
<br>
Jon Evans, PE<br>
<br>
Sustainable Engineering Group LLC<br>
431 Charmany Drive Suite 102<br>
Madison, WI 53719<br>
<br>
Tel: (608) 231 9664 x 13<br>
Fax: (608) 231 9665<br>
<br>
E-mail: <a href="mailto:jevans@sustaineng.com">jevans@sustaineng.com</a><br>
Web: <a href="http://www.sustaineng.com" target="_blank">www.sustaineng.com</a><br>
<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote></div><br><br clear="all"><br><br>