<DIV>Mehta/Demba,</DIV>
<DIV> </DIV>
<DIV>Before taking the approach of increasing "the proportion of your space that benefits from daylighting as a result of the deeper light penetration allowed by the shelves," you should use a detailed daylight simulation program to determine if any extra credit should be attributed to your chosen light shelves. Though conceptual renderings and many designers tend to suggest there is great deep daylight benefit, most daylighting experts suggest the real benefits to be the reduction in direct solar radiation striking occupants and the fact that the bounced light dispels shadows/contrast areas on the ceiling near the window, enhancing the overall ambient lighting of the space.</DIV>
<DIV> </DIV>
<DIV>Regards,</DIV>
<DIV><BR>Paul<BR></DIV>
<DIV> </DIV>
<DIV>
<DIV><FONT size=2>Paul Erickson</FONT></DIV>
<DIV><FONT size=2>Sustainable Team Leader</FONT></DIV>
<DIV><FONT size=2>Affiliated Engineers, Inc</FONT></DIV>
<DIV><A href="http://www.aeieng.com/"><FONT size=2>www.aeieng.com</FONT></A></DIV>
<DIV><FONT size=2>608.236.1112</FONT></DIV>
<DIV><FONT size=2>303.859.7523 - c</FONT></DIV>
<DIV>
<DIV>
<DIV><A href="mailto:mschrader@aeieng.com"></A></DIV><FONT face=Arial></FONT></DIV>
<DIV>
<DIV><SPAN lang=NL style="FONT-SIZE: 13.5pt; COLOR: green; FONT-FAMILY: Webdings">P</SPAN><FONT face=Verdana color=navy size=2><SPAN lang=NL style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Verdana"> </SPAN></FONT><FONT face=Verdana color=green size=1><SPAN style="FONT-SIZE: 7.5pt; COLOR: green; FONT-FAMILY: Verdana">P</SPAN></FONT><FONT face=Verdana color=green size=1><SPAN lang=NL style="FONT-SIZE: 7.5pt; COLOR: green; FONT-FAMILY: Verdana">lease consider the environment before printing this</SPAN></FONT><FONT face=Verdana color=navy size=2><SPAN lang=NL style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Verdana"> </SPAN></FONT><FONT face=Verdana color=green size=1><SPAN style="FONT-SIZE: 7.5pt; COLOR: green; FONT-FAMILY: Verdana">message.</SPAN></FONT></DIV></DIV></DIV><BR><BR>>>> "Demba Ndiaye" <Demba.Ndiaye@uoit.ca> 11/20/2008 4:45 PM >>><BR>One possibility is to model daylighting as usual and increase the<BR>proportion of your space that benefits from the daylighting as a result<BR>of the deeper light penetration allowed by the shelves.<BR><BR>_____________<BR>Demba Ndiaye<BR><BR>-----Original Message-----<BR>From: equest-users-bounces@lists.onebuilding.org<BR>[mailto:equest-users-bounces@lists.onebuilding.org] On Behalf Of Howe,<BR>Timothy<BR>Sent: Thursday, November 20, 2008 5:21 PM<BR>To: Amol Mehta; equest-users@lists.onebuilding.org<BR>Subject: Re: [Equest-users] Light Shelves<BR><BR>Not possible as of yet. <BR><BR>-----Original Message-----<BR>From: equest-users-bounces@lists.onebuilding.org<BR>[mailto:equest-users-bounces@lists.onebuilding.org] On Behalf Of Amol<BR>Mehta<BR>Sent: Thursday, November 20, 2008 5:17 PM<BR>To: equest-users@lists.onebuilding.org<BR>Subject: [Equest-users] Light Shelves<BR><BR>Hi <BR><BR>I am trying to model Light Shelves in E-Quest for day lighting. Can you<BR>please help me on this? Thanks<BR><BR><BR>Amol Mehta | Mechanical Engineer | P2S Engineering, Inc.<BR>T 562 497 2999 | F 562 497 2990 | M 858 354 6250 5000 East Spring<BR>Street, 8th Floor, Long Beach, CA 90815 -----Original Message-----<BR>From: equest-users-bounces@lists.onebuilding.org<BR>[mailto:equest-users-bounces@lists.onebuilding.org] On Behalf Of<BR>equest-users-request@lists.onebuilding.org<BR>Sent: Thursday, November 20, 2008 12:04 PM<BR>To: equest-users@lists.onebuilding.org;<BR>equest-users@lists.onebuilding.org;<BR>equest-users@lists.onebuilding.org; equest-users@lists.onebuilding.org<BR>Subject: Equest-users Digest, Vol 8, Issue 22<BR><BR>Send Equest-users mailing list submissions to<BR>equest-users@lists.onebuilding.org<BR><BR>To subscribe or unsubscribe via the World Wide Web, visit<BR><BR><A href="http://lists.onebuilding.org/listinfo.cgi/equest">http://lists.onebuilding.org/listinfo.cgi/equest</A>-users-onebuilding.org<BR><BR>or, via email, send a message with subject or body 'help' to<BR>equest-users-request@lists.onebuilding.org<BR><BR>You can reach the person managing the list at<BR>equest-users-owner@lists.onebuilding.org<BR><BR>When replying, please edit your Subject line so it is more specific than<BR>"Re: Contents of Equest-users digest..."<BR><BR><BR>Today's Topics:<BR><BR> 1. PIU vs. VAV in eQuest (Matthew Dubrovich)<BR> 2. Re: PIU vs. VAV in eQuest (Kevin Madison)<BR><BR><BR>----------------------------------------------------------------------<BR><BR>Message: 1<BR>Date: Thu, 20 Nov 2008 09:06:50 -0700<BR>From: "Matthew Dubrovich" <mdubrovich@emcengineers.com><BR>Subject: [Equest-users] PIU vs. VAV in eQuest<BR>To: <equest-users@lists.onebuilding.org><BR>Message-ID:<BR><216F285E03BAC04B9F6E6F17D4C7405E121B6684@VS6.EXCHPROD.USA.NET><BR>Content-Type: text/plain; charset="us-ascii"<BR><BR>For those that are on both the BLDG-SIM and this list, I apologize for<BR>the repost...<BR><BR><BR><BR><BR><BR>Question on PIU vs. VAV systems in eQuest...<BR><BR><BR><BR>If a PIU system has only SVAV boxes and all other parameters are<BR>identical, does the PIU act like a VAV in eQuest? Only changing the<BR>system type in my model seems to have a significant impact on energy<BR>usage and I can't track down why that is. The difference is significant<BR>enough that with App. G System 7 VAV w/RH, the choice between PIU and<BR>VAV has an effect on the number of points. Any thoughts would be<BR>appreciated.<BR><BR><BR><BR><BR><BR>Thanks,<BR><BR><BR><BR>Matt<BR><BR><BR><BR>-------------- next part --------------<BR>An HTML attachment was scrubbed...<BR>URL:<BR><<A href="http://lists.onebuilding.org/pipermail/equest">http://lists.onebuilding.org/pipermail/equest</A>-users-onebuilding.org/att<BR>achm<BR>ents/20081120/aef3cb03/attachment.html><BR><BR>------------------------------<BR><BR>Message: 2<BR>Date: Thu, 20 Nov 2008 09:00:21 -0800<BR>From: Kevin Madison <kevinjm5000@yahoo.com><BR>Subject: Re: [Equest-users] PIU vs. VAV in eQuest<BR>To: Matthew Dubrovich <mdubrovich@emcengineers.com><BR>Cc: equest-users@lists.onebuilding.org<BR>Message-ID: <492597A5.50208@yahoo.com><BR>Content-Type: text/plain; charset=windows-1252; format=flowed<BR><BR>Matt -<BR>You may be observing the result of the different default for<BR>"THERMOSTAT-TYPE" for zones served by each system. The default for VAVS<BR>is "REVERSE-ACTION" while it is "PROPORTIONAL" for PIU. Take a look in<BR>the DOE-2 documentation for descriptions of each of these and how this<BR>property affects ZONE terminal unit and SYSTEM operation.<BR>- Kevin<BR><BR>Kevin Madison<BR>Madison Engineering PS<BR>Seattle WA<BR><BR><BR>Matthew Dubrovich wrote:<BR>><BR>> For those that are on both the BLDG-SIM and this list, I apologize for<BR><BR>> the repost?<BR>><BR>> Question on PIU vs. VAV systems in eQuest?<BR>><BR>> If a PIU system has only SVAV boxes and all other parameters are <BR>> identical, does the PIU act like a VAV in eQuest? Only changing the <BR>> system type in my model seems to have a significant impact on energy <BR>> usage and I can?t track down why that is. The difference is <BR>> significant enough that with App. G System 7 VAV w/RH, the choice <BR>> between PIU and VAV has an effect on the number of points. Any <BR>> thoughts would be appreciated.<BR>><BR>> Thanks,<BR>><BR>> Matt<BR>><BR>> ----------------------------------------------------------------------<BR>> --<BR>><BR>> _______________________________________________<BR>> Equest-users mailing list<BR>> <A href="http://lists.onebuilding.org/listinfo.cgi/equest">http://lists.onebuilding.org/listinfo.cgi/equest</A>-users-onebuilding.org<BR>> To unsubscribe from this mailing list send a blank message to<BR>EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR>> <BR><BR><BR>------------------------------<BR><BR>_______________________________________________<BR>Equest-users mailing list<BR>Equest-users@lists.onebuilding.org<BR><A href="http://lists.onebuilding.org/listinfo.cgi/equest">http://lists.onebuilding.org/listinfo.cgi/equest</A>-users-onebuilding.org<BR><BR><BR>End of Equest-users Digest, Vol 8, Issue 22<BR>*******************************************<BR><BR><BR><BR>_______________________________________________<BR>Equest-users mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/equest">http://lists.onebuilding.org/listinfo.cgi/equest</A>-users-onebuilding.org<BR>To unsubscribe from this mailing list send a blank message to<BR>EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR><BR>_______________________________________________<BR>Equest-users mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/equest">http://lists.onebuilding.org/listinfo.cgi/equest</A>-users-onebuilding.org<BR>To unsubscribe from this mailing list send a blank message to<BR>EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR><BR>_______________________________________________<BR>Equest-users mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/equest">http://lists.onebuilding.org/listinfo.cgi/equest</A>-users-onebuilding.org<BR>To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR></DIV></BODY></HTML>