<div dir="ltr">Ok, so there are a few challenges in trying to model this system. I would be cautious about splitting the zone and using an air wall, because this may result in heating loads on one side and cooling loads on the other, when really the space would balance itself, you just need to be careful about where to make the delineation. I have split zones to model buildings that have radiant heat under windows. In this case, I've created a perimiter zone a few feet deep which is heated by a HW baseboards, and it seemed to work ok.<br>
<br>Another option is to just put HW baseboards in, along with the water-to-air heat pump. I believe the baseboards will pick up almost all the heating load and am not sure if there is a way to specify that the air system pick up some load as well. Here's the problem with this plan: eQuest's loop-to-loop heat pumps don't work with WLHP or GLHP loops. They do work with loops of type lake/well. You can schedule lake/well temperatures, so you could run the building with a straight air-to-air heat pump system, and track GLHP loop temperature. By averaging the monthly or weekly loop temperature, you can create a temp schedule for a lake/well loop. Then re-model as I've described and run both water-to-air and water-to-water heat pumps off this loop.<br>
<br>Last option is to specify an air-to-air heat pump system only and adjust your heating efficiency and performance curves to approximate a water-to-water heat pump. This method overlooks a couple things: <br><br>1. no HW loop is simulated so the pressure drop through the system in the zone is modeled as being the same regardless of whether you are in heating or cooling mode, and pumping energy is not modeled as well as could be<br>
2. fan power is specified once, you can't get rid of the fan power during heating hours, although you could subtract this value on an hourly report schedule<br><br>I would try the lake/well loop with baseboards. This seems to be the closest approximation. Good luck and let me know how it goes--I'm curious.<br>
<br><br>--<br>Karen<br>