<div dir="ltr">Sam-<br><br>Your subject said the best way.  Just model your side of the building that is touching another building as an interior wall facing into the same space.  It will automatically make that an adiabatic wall and stop the heat transfer.<br>
<br><br>-- <br>Steve Mignogna<br>Atelier Ten<br><br><div class="gmail_quote">On Thu, Sep 11, 2008 at 4:32 PM, Sam Alpert <span dir="ltr"><<a href="mailto:Sam.Alpert@gdsassociates.com">Sam.Alpert@gdsassociates.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">



<div>
<div><font face="Arial" size="2"><span>Is there a way to 
model a building with one side or one wall touching another building or another 
conditioned space?</span></font></div>
<div><font face="Arial" size="2"><span></span></font> </div>
<div><font face="Arial" size="2"><span>Reducing the air 
leakage rate would be one option but I am not the best person to be able to 
estimate that air leakage reduction.</span></font></div>
<div><font face="Arial" size="2"><span></span></font> </div>
<div><font face="Arial" size="2"><span>Thanks for the 
help,</span></font></div>
<table bgcolor="#ffffff" border="1" cellpadding="0" cellspacing="0" width="300">
  <tbody>
  <tr>
    <td height="145" width="300">
      <table border="0" cellpadding="5" cellspacing="0" width="300">
        <tbody>
        <tr>
          <td style="font-size: 7pt; font-family: Tahoma;" align="center" width="150"><a href="http://www.gdsassociates.com/" target="_blank"><img alt="www.gdsassociates.com" src="http://www.gdsassociates.com/images/gdscardlogo.jpg" border="0" height="65" width="60"></a><br>
<br><b>GDS Associates, Inc.</b><br>Engineers and 
            Consultants</td>
          <td style="font-size: 7pt; font-family: Tahoma;" align="center" width="149"><b>SAMUEL M. ALPERT, 
            CEM</b><br><b>Engineer</b><br><br>1181 Elm Street, Suite 
            205<br>Manchester, NH 03101<br>phone 603.656.0336<br>fax 
            603.656.0301<br>cell 603-296-5308<br><a href="mailto:Sam.Alpert@gdsassociates.com" target="_blank">Sam.Alpert@gdsassociates.com</a><br></td></tr></tbody></table></td></tr></tbody></table><br>
<div> </div></div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>
</div>