<div dir="ltr">Dan-<br><br>To change the roof manually, you will need to edit the polygon it references.  I would recommend making a copy of the polygon and change the dimensions in there.  Then re-reference your roof polygon to the newly created one.<br>
<br>To add exterior lighting, I always input it in terms of kW and not W/ft2.  To do this, you need to input it as a "direct load" in your electric meter.  There is a box for "exterior direct loads" and you can input the kW and assign an exterior lighting schedule there.  I would also assign the enduse as "exterior usage."<br>
<br>Both of these are down outside of the wizard.  Good luck.<br><br>-- <br>Steve Mignogna<br>Atelier Ten<br><br><br><br><br><div class="gmail_quote">On Wed, Aug 13, 2008 at 11:40 AM, Daniel Wilkerson <span dir="ltr"><<a href="mailto:DWilkerson@dwyer.com">DWilkerson@dwyer.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">









<div link="blue" vlink="purple" lang="EN-US">

<div>

<p><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">Hey all,</span></font></p>

<p><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>

<p><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">On screen 23 of the DD wizard, the Exterior Lighting Load is
to be entered in units of Watts per square foot, but what area is the square
footage referencing—outdoor area or indoor area or…?  Also, I
have a three story building where the two upper floors have a smaller footprint
than the first and thus I have to create partial roofs; I am trying to do it in
detailed edit mode per somebody's suggestion, but the "Height"
and "Width" fields have a gray "n/a" in them and
numbers can't be entered… am I going about creating roofs
incorrectly?  Thanks,</span></font></p>

<p><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>

<p><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;">     -Dan</span></font></p>

<p><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>

<p><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"><img height="561" width="754"></span></font></p>

<p><font face="Arial" size="2"><span style="font-size: 10pt; font-family: Arial;"><img height="557" width="460"></span></font></p>

</div>

</div>


<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br><br>
</div>