<BODY style="MARGIN: 4px 4px 1px; FONT: 10pt Tahoma">No, that's not required. If the WSE-"Chiller" is listed with the chillers on a loop, DOE-2 will use it when conditions allow. "Conditions" include CHW temperature, so reset up of CHW if possible maximizes the modeled use of the WSE. <BR><BR>>>> Brian Fountain <bfountain@greensim.com> 7/28/2008 2:12 PM >>><BR>Further to this -- you will likely need to set up your equipment <BR>controls to specify the water economizer chiller type leading in the <BR>winter (below a certain OA) and the regular chillers leading above a <BR>certain OA -- or based on a schedule.<BR><BR>Steve Mignogna wrote:<BR>> You can set up a separate chiller of type "water economizer". This <BR>> will attach to your CHW and CW Loops and will bypass the chiller and <BR>> circulate through your cooling tower when the outside air conditions <BR>> are acceptable for free cooling.<BR>><BR>><BR>><BR>> On Fri, Jul 25, 2008 at 11:13 AM, Marcus Eliason <meliason@essexco.com <BR>> <mailto:meliason@essexco.com>> wrote:<BR>><BR>><BR>> Hello,<BR>><BR>> Can someone please explain the proper way to model a waterside<BR>> economizer in<BR>> eQuest? I have found the option for a cooling tower with HX, but<BR>> this does<BR>> not seem to yield any results.<BR>><BR>> Thank you,<BR>><BR>> Marcus Eliason<BR>> Essex Engineering Corporation<BR>> 404.365.9482<BR>> meliason@essexco.com <mailto:meliason@essexco.com><BR>><BR>><BR>> _______________________________________________<BR>> Equest-users mailing list<BR>> <A href="http://lists.onebuilding.org/listinfo.cgi/equest">http://lists.onebuilding.org/listinfo.cgi/equest</A>-users-onebuilding.org<BR>> To unsubscribe from this mailing list send a blank message to<BR>> EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR>> <mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG><BR>><BR>><BR>><BR>><BR>> -- <BR>> Steve Mignogna<BR>> Atelier Ten<BR>> ------------------------------------------------------------------------<BR>><BR>> _______________________________________________<BR>> Equest-users mailing list<BR>> <A href="http://lists.onebuilding.org/listinfo.cgi/equest">http://lists.onebuilding.org/listinfo.cgi/equest</A>-users-onebuilding.org<BR>> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR>> <BR>> ------------------------------------------------------------------------<BR>><BR>> No virus found in this incoming message.<BR>> Checked by AVG. <BR>> Version: 7.5.524 / Virus Database: 270.5.5/1570 - Release Date: 7/24/2008 6:59 AM<BR>> <BR><BR>_______________________________________________<BR>Equest-users mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/equest">http://lists.onebuilding.org/listinfo.cgi/equest</A>-users-onebuilding.org<BR>To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG<BR></BODY></HTML>