Report SS-R gives the number of hours the fans are in each part load range. Generally, with heat pumps, the minimum fan ratio is 1, which means that the heat pump fans cycle on (100%), then off (0%). So the report is correct. If you have variable speed fans for this system, you need to change your input parameters to allow the fans to cycle at less than 100%.<br>
<br>--<br>Karen<br><br><div class="gmail_quote">On Tue, Jul 8, 2008 at 11:00 AM, Alison Staudinger <<a href="mailto:astaudinger@jdrm.com">astaudinger@jdrm.com</a>> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
<div link="blue" vlink="purple" lang="EN-US">
<div>
<p>I'm stumped...</p>
<p> </p>
<p>I let eQuest select the size of my heat pumps, but when I
look at the SS-R report to see my unmet hours and part load performance every heat
pump is operating at maximum capacity. Not a single unit has any part
load performance. I would think this could happen if I selected the size
of the units, but if the program is sizing it, wouldn't it select a unit
that is large enough to meet capacity which would have to result in some part
load performance? There are some units that have many unmet hours (typically
heating) and others that have no unmet hours. Both cases have no part
load hours. Any input would be appreciated.</p>
<p> </p>
<p>Thanks!</p>
<p> </p>
<p><b><span style="font-size: 10pt;">Alison
Staudinger P.E., LEED AP</span></b><span></span></p>
<p><span style="font-size: 10pt;">JDRM
Engineering</span><span></span></p>
<p><span style="font-size: 10pt;">5604
N. Main St.</span><span></span></p>
<p><span style="font-size: 10pt;">Sylvania,
OH 43560</span><span></span></p>
<p><span style="font-size: 10pt;">(419)
824-2400</span></p>
<p> </p>
</div>
</div>
<p align="left"><font face="Tahoma" size="2"><font color="#0000ff">--| Any project file attachments should be sent to <a href="mailto:files@jdrm.com" target="_blank">files@jdrm.com</a></font></font></p>
<p align="left"><font color="#0000ff" face="Tahoma" size="2">--| This mail and all information contained herein is the property</font></p>
<p align="left"><font color="#0000ff" face="Tahoma" size="2">--| of JDRM Engineering, Inc. for use by the intended recipient only !</font></p>
<p align="left"><font color="#0000ff" face="Tahoma" size="2">--| Copyright (c) 2008 JDRM Eng, Inc. All Rights Reserved.</font></p>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br>