Additional answers -<br>
1 - The estimated CHW load info on the Cooling Primary Equipment screen
is designed as a convenient mechanism to enable the user to calculate a
total required cooling tons.  The resultant (estimated) # tons is then
used to default and number of chillers and chiller size range further
down on the screen, but that is it.<br>
<br>
2 - Cooling tower inputs (and the corresponding cooling tower in the
detailed model) will be eliminated by selecting an air-cooled chiller
within the wizard.  This will make your detailed interface changes,
where you replace the chiller(s) and boiler(s) w/ CHW & Steam
meters as Vikram described, a little bit easier.<br>
<br>
3 - Custom electric and gas rates can be entered in the wizard by
choosing "- custom -" for the selections of Electric & Gas
Utilities on the first (Project / Site / Utility) DD wizard screen,
which then activate screens 4-6 of the proj/site/util screens where the
custom rate data can be entered.  Further information can be found in a
text file and PDF found in the \Rates subdirectory of your eQUEST
program directory.<br>
<br>
- Scott<br>
<br>
<br>
Vikram Sami wrote:
<blockquote
 cite="mid:55BA83825A482144A8637F9CAA981F76101483F2@las-mail.lordaecksargent.internal"
 type="cite">
  <meta http-equiv="Content-Type" content="text/html; ">
  <meta content="MSHTML 6.00.6000.16640" name="GENERATOR">
  <div dir="ltr" align="left"><span class="106071620-30042008"><font
 color="#0000ff" face="Arial" size="2">I typically do this in the
detailed interface. What you need to do is set up a chilled water and
steam meter with a respective utility rate for each of them. In the
water side tab you will need to assign the chilled water meter to the
chilled water loop, and the steam/ hot water meter to the hot water
loop.</font></span></div>
  <div dir="ltr" align="left"><span class="106071620-30042008"></span> </div>
  <div dir="ltr" align="left"><span class="106071620-30042008"><font
 color="#0000ff" face="Arial" size="2">For the water heater question -
I assume you will want to select the electric option in the heater
type. </font></span></div>
  <div> </div>
  <div><span class="106071620-30042008"><font color="#0000ff"
 face="Arial" size="2">Hope this helps</font></span></div>
<!-- Converted from text/rtf format -->
  <p><b><font color="#000000" face="Garamond">Vikram Sami,</font></b> <font
 color="#000000" face="Garamond">LEED AP</font> <br>
  <font color="#000000" face="Garamond">Direct Phone 404-253-1466 |
Direct Fax 404-253-1366</font> </p>
  <p><b><font color="#800000" face="Garamond">L</font><font
 color="#800000" face="Garamond" size="2">ORD</font><font
 color="#800000" face="Garamond">, A</font><font color="#800000"
 face="Garamond" size="2">ECK</font><font color="#800000"
 face="Garamond"> & S</font><font color="#800000" face="Garamond"
 size="2">ARGENT</font><font color="#800000" face="Garamond"> A</font><font
 color="#800000" face="Garamond" size="2">RCHITECTURE</font><br>
  </b><font face="Garamond" size="2">1201 Peachtree Street NE, Suite
300, Atlanta, GA 30361</font> <br>
  <font face="Garamond" size="2">Responsive Design</font> <font
 face="Symbol" size="1">·</font> <font face="Garamond" size="2">Technological
Expertise</font> <font face="Symbol" size="1">·</font> <font
 face="Garamond" size="2">Exceptional Service</font> <br>
  <font color="#000000" face="Garamond"><a class="moz-txt-link-abbreviated" href="http://www.lordaecksargent.com">www.lordaecksargent.com</a></font> </p>
  <p><b><font color="#008000" face="Garamond">Please don't print this
email unless you really have to</font></b><i><font color="#008000"
 face="Garamond">.</font></i> <br>
  <i><font color="#008000" face="Garamond">In the United States, we use
enough office paper each year to build a 10-foot high wall that’s 6,815
miles long or two and a half times the distance from New York to Los
Angeles. </font></i></p>
  <p><i><font color="#008000" face="Garamond">~ Wisconsin Department of
Natural Resources, “Recycling Facts and Figures,” PUBL CE-163, 2002.</font></i>
  </p>
  <div> </div>
  <br>
  <div class="OutlookMessageHeader" dir="ltr" align="left" lang="en-us">
  <hr tabindex="-1"><font face="Tahoma" size="2"><b>From:</b>
<a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Jim
Weiner<br>
  <b>Sent:</b> Wednesday, April 30, 2008 3:41 PM<br>
  <b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
  <b>Subject:</b> [Equest-users] Fwd: Questions to input/select
conditions in e-quest(district plant)<br>
  </font><br>
  </div>
  <div class="gmail_quote">hoping the visuals work for this...<br>
We are modeling a 17 story office building in Tokyo that draws power
from a district plant and have basic questions about setting up per the
attached screenshots. We would also find direction to a guidance for
entering custom rate schedules for fuel costs useful.<br>
  <br>
many thanks - j<br>
  <font color="#888888"><br>
-- <br>
James Weiner, AIA<br>
Collaborative Project Consulting<br>
  <br>
  </font></div>
  <br>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
  </pre>
</blockquote>
</body>
</html>