Hi Chris,

Are you running DOE2.2 or DOE2.3?

Looking through the DOE2.2 Vol2 Dictionary, there is a note that, “the performance curves are normalized at the Eurovent rating conditions, rather than ARI.” For HEAT-EIR-FT, “this curve should be normalized to 1.0 at the ARI or Eurovent rating point” but I don’t know what temp that is (or was, in 2009).

With DOE2.3, HEAT-EIR-FT, “the value of the curve is usually normalized to 1.0 at rated conditions, but this is not mandatory; the program will normalize the curve internally”.
In DOE2.3 mode, the default value for RATED-COND-T-HT is 45F based on the default expression for an air-cooled condenser. The default for RATED-HW-T is 110F.
You can experiment by creating a custom hourly report block with variable type Chiller that reports leaving supply temperature, entering condenser temperature and correction to heat-input-ration for temperature.

Regards,
~Bill


William Bishop, PE, CEM, LEED AP, ASHRAE (BEMP, BEAP, CDP)
IMEG | Associate Principal | Project Executive | Sustainability & Energy
[IMEG]<https://www.imegcorp.com/>

134 South Fitzhugh Street | Rochester | NY, 14608
Military Veteran Employee | LinkedIn Profile<%3c!--liURL--%3e> | vCard<%3c!--vcardURL--%3e>

website<https://www.imegcorp.com> | map<https://www.google.com/maps/place/Pathfinder+Engineers+%26+Architects+LLP/@43.1504815,-77.6145058,17z/data=!3m1!4b1!4m6!3m5!1s0x89d6b4fe9e48aab1:0x6991ae3d559d5aee!8m2!3d43.1504776!4d-77.6119309!16s%2Fg%2F1tcw955j?hl=en&entry=ttu%3c!--mapURL--%3e> | IMEG News<https://imegcorp.com/about/news-events/>
[X, formerly Twitter]<http://twitter.com/IMEGcorp>[Facebook]<https://www.facebook.com/IMEGcorp/>[LinkedIn]<https://www.linkedin.com/company/imeg-corp>

Learn more<https://www.imegcorp.com/about/our-story/> about us and the IMEG story!


From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Chris Hadlock via Equest-users
Sent: Wednesday, May 20, 2026 10:20 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Heat Pump Chiller - Anyone know the Rating Conditions

External Email: Treat links and attachments with caution.
Hi All,

I'm modeling a "heat pump" type chiller (air-cooled) and I'm trying to figure out the dependent variables about which the default curves are normalized so that I can create my own curves. Below is the screen-shot for my heat pump Performance Curves.
[cid:image001.png at 01DCE887.42E364E0]
For example, the heating EIR curve that is a function of evap leaving T (SWT) & cond entering T (OAT): does anyone know the leaving water temperature and entering air temperature at which point this curve is normalized (i.e. returns an EIR value of 1.000)? I used goal seek for various combination of temperatures and here are some options (yellow cell was calculated using GOAL-SEEK ):

SWT ->
120
115
115.6816
105
112.2388
OAT ->
54.36586
61.10728
47
39.21
44
Goal Seek set to 1.000 ->
1.003649
0.999675
0.99995
1
0.999975

Based on these results, it's looking like perhaps 115F SWT and 47F OAT might be correct...but wanted to confirm.

Since there is a second heating EIR curve for OAT < 39F, does anyone know the leaving water temperature and entering air temperature at which point this curve is normalized?

Thanks,
Chris
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20260520/2b85e9d5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 32144 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20260520/2b85e9d5/attachment.png>


More information about the Equest-users mailing list