[Equest-users] Here is a real knuckle ball

Brian Fountain bfountain at greensim.com
Thu Jun 19 20:14:13 PDT 2025


I am not seeing what you are seeing.  With no lighting, space heat is 239,761 kWh.  With lighting,  space heating is 174,860 kWh. Cooling is also behind as I would expect ... more with lighting. 

I think your lighting schedule is dramatically too big for apartments. It ranges from 60% overnight all night to high 80s all day. I wouldn't expect more than 3 to 4 hours of lighting for apartments. 

On Jun 19, 2025, 6:27 p.m., at 6:27 p.m., John Aulbach <jra_sac at yahoo.com> wrote:
>I attach two versions of a Multi family project I am working on in
>Virginia, plus the weather I used. DETAIL-1 is the way I ran it was
>normal, an individual heat pump in hundreds of zones. My Client feels
>the space heating load is not enough and feels eQuest is
>overcompensating for the heat emitted by LEDs vs the fluorescent light
>actually represented.
>So I thought, what if I removed the lighting COMPLETELY, to see how
>much space heating would go up.
>But, golly, space heating went DOWN (see attached BEPS from each model)
>!!
>What physics course did I miss to explain THIS one??
>John R Aulbach, PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20250619/0a112a03/attachment.htm>


More information about the Equest-users mailing list