[Equest-users] Here is a real knuckle ball
Brian Fountain
bfountain at greensim.com
Thu Jun 19 20:14:13 PDT 2025
I am not seeing what you are seeing. With no lighting, space heat is 239,761 kWh. With lighting, space heating is 174,860 kWh. Cooling is also behind as I would expect ... more with lighting.
I think your lighting schedule is dramatically too big for apartments. It ranges from 60% overnight all night to high 80s all day. I wouldn't expect more than 3 to 4 hours of lighting for apartments.
On Jun 19, 2025, 6:27 p.m., at 6:27 p.m., John Aulbach <jra_sac at yahoo.com> wrote:
>I attach two versions of a Multi family project I am working on in
>Virginia, plus the weather I used. DETAIL-1 is the way I ran it was
>normal, an individual heat pump in hundreds of zones. My Client feels
>the space heating load is not enough and feels eQuest is
>overcompensating for the heat emitted by LEDs vs the fluorescent light
>actually represented.
>So I thought, what if I removed the lighting COMPLETELY, to see how
>much space heating would go up.
>But, golly, space heating went DOWN (see attached BEPS from each model)
>!!
>What physics course did I miss to explain THIS one??
>John R Aulbach, PE