Margaret,
It is difficult to say based on the information provided. Did you adjust
the RUN-PERIOD for your model at all?
I would suggest verifying the following 3 bullet points for each of your
schedules under the Annual Schedules section of your .inp file, or
verifying the equivalent data within each of the Annual Schedules in the
eQUEST interface:
- The last value listed for MONTH is the same as your RUN-PERIOD
END-MONTH
- The last value listed for DAY is the same as your RUN-PERIOD END-DAY
- The lists of values for MONTH, DAY, and WEEK-SCHEDULES are all the
same length
Example below.
$ ---------------------------------------------------------
$ Title, Run Periods, Design Days, Holidays
$ ---------------------------------------------------------
"Entire Year" = RUN-PERIOD-PD
BEGIN-MONTH = 1
BEGIN-DAY = 1
BEGIN-YEAR = 2021
END-MONTH = 12
END-DAY = 31
END-YEAR = 2021
..
$ ---------------------------------------------------------
$ Annual Schedules
$ ---------------------------------------------------------
"Kitchen Cool Sch" = SCHEDULE-PD
TYPE = TEMPERATURE
MONTH = ( 1, 5, 5, 6, 6, 7, 7, 8, 8, 9, 9, 10, 10, 12, 12 )
DAY = ( 7, 1, 8, 1, 8, 1, 8, 1, 8, 1, 8, 1, 8, 24, 31 )
WEEK-SCHEDULES = ( "OFF Cool WK", "Kitchen Market Cool Wk",
"Kitchen Event Cool Wk", "Kitchen Market Cool Wk",
"Kitchen Event Cool Wk", "Kitchen Market Cool Wk",
"Kitchen Event Cool Wk", "Kitchen Market Cool Wk",
"Kitchen Event Cool Wk", "Kitchen Market Cool Wk",
"Kitchen Event Cool Wk", "Kitchen Market Cool Wk",
"Kitchen Event Cool Wk", "Kitchen Market Cool Wk", "OFF Cool WK" )
..
"Market Heat Sch" = SCHEDULE-PD
TYPE = TEMPERATURE
MONTH = ( 1, 5, 5, 6, 6, 7, 7, 8, 8, 9, 9, 10, 10, 12, 12 )
DAY = ( 7, 1, 8, 1, 8, 1, 8, 1, 8, 1, 8, 1, 8, 24, 31 )
WEEK-SCHEDULES = ( "OFF Heat WK", "Market Heat WK", "Event Heat Wk",
"Market Heat WK", "Event Heat Wk", "Market Heat WK",
"Event Heat Wk", "Market Heat WK", "Event Heat Wk",
"Market Heat WK", "Event Heat Wk", "Market Heat WK",
"Event Heat Wk", "Market Heat WK", "OFF Heat WK" )
..
*Jackson Jarboe* PE, LEED AP
Senior Energy Engineer
[image: image.png]
Work 860.430.9995
We are always looking for motivated professionals to join our team. See our
career options here <https://karpmanconsulting.net/available-careers>!
On Wed, Feb 5, 2025 at 12:00 PM Margaret Stadlman via Equest-users <
equest-users at lists.onebuilding.org> wrote:
> Good afternoon, I am having this issue when I try to run my model, I have
> looked around in my file a bit and nothing seems amiss. Does anyone else
> have an idea of what annual schedule it is referring to?
>
>
>
>
>
> <https://thriven.design/>
>
> *Margaret Stadlman*
>
> Engineering Contributor
> ------------------------------
>
> mstadlman at thriven.design
>
> *t:* 856.854.1880 x128 <856.854.1880%20x128> | *d:* 856.559.2028
>
> 756 Haddon Ave. Collingswood, NJ 08108
>
> <https://www.linkedin.com/company/thrivendesign>
> <https://www.instagram.com/thriven.design/>
> <https://www.facebook.com/thriven.design/>
>
> *thriven.design* <https://thriven.design/>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20250205/694b86fd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 18883 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20250205/694b86fd/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 1811 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20250205/694b86fd/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 1899 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20250205/694b86fd/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1581 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20250205/694b86fd/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 9335 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20250205/694b86fd/attachment-0004.png>
More information about the Equest-users
mailing list