[Equest-users] eQuest Error on Opening - Invalid Previous Run Date

Christina LaPerle christina at karpmanconsulting.net
Thu Dec 18 05:56:27 PST 2025


P.S. This fix is not needed when opening eQUEST in DOE-2.3 mode, but needs
to be applied after any open in DOE-2.2 mode even when that open was just
to switch to DOE-2.3 mode.

*Christina LaPerle (she/her)* PE, BEMP, CPHC®, CEM, CBCP
Principal Engineer
________________
[image: image.png]
Phone 860.266.6220
We are always looking for motivated professionals to join our team. See our
career options here <https://karpmanconsulting.net/available-careers>!
*PTO Alert: ** Out after 12/19/2025 and back 1/2/2025*


On Thu, Dec 18, 2025 at 8:52 AM Christina LaPerle <
christina at karpmanconsulting.net> wrote:

> Hi Everyone,
>
> Temporary solution for DOE-2.2 per communication with Jeff (it works I
> tried it).
>
> In the equest.ini, in the [Registration} section at the bottom, if you set
> Status=0
> before stating eQUEST, when DOE-2.2 is selected for the simulation engine
> (not an issue with DOE-2.3 selected), should cause a registration dialog
> with a valid registration number to be displayed instead, then you should
> be able to click OK and it should startup normally. Some suggested using
> the original equest.ini before starting it the first time and setting the
> file to be read only; but that prevents saving other information about the
> last use rather than having the startup just ignore previous date
> information.
>
> Applies eQUEST.ini located in the C:\Users\"your user
> name"\Documents\eQUEST 3-65-7175 Data\
>
> You can keep it open in Notepad and just reset the status to 0 each time
> before re-opening eQUEST.
>
> *Christina LaPerle (she/her)* PE, BEMP, CPHC®, CEM, CBCP
> Principal Engineer
> ________________
> [image: image.png]
> Phone 860.266.6220
> We are always looking for motivated professionals to join our team. See
> our career options here <https://karpmanconsulting.net/available-careers>!
> *PTO Alert: ** Out after 12/19/2025 and back 1/2/2025*
>
>
> On Thu, Dec 18, 2025 at 7:42 AM Daric Adair <
> Daric.Adair at hendersonengineers.com> wrote:
>
>> My team started having issues after a Windows 11update. Not everyone, but
>> most.
>>
>> Kidding / not-kidding – the covert effort to kill off eQuest continues…..
>>
>>
>>
>> Thanks,
>>
>> *DARIC ADAIR*
>>
>>
>>
>> PE, BEMP, CEM
>>
>> ​​​​
>>
>> Energy Modeling Manager
>>
>> Strategic Consulting Sector
>>
>> *Henderson Companies | *
>>
>> *Employee Owned
>> <https://www.hendersonengineers.com/employee-owned/?utm_source=Signature&utm_medium=Email&utm_campaign=Short_Engineers>*
>>
>> *TEL (913) 742-5530 <(913)%20742-5530>*
>>
>> *LICENSED IN* KS
>>
>>
>>
>>
>>
>> *From:* Jeff Ross-Bain <jeff at rbgb.com>
>> *Sent:* Wednesday, December 17, 2025 2:59 PM
>> *To:* Christina LaPerle <christina at karpmanconsulting.net>; Rahil Shah <
>> rahil at nyu.edu>
>> *Cc:* equest-users at lists.onebuilding.org; Melissa Crowe <
>> melissa.crowe at oakwellteam.com>
>> *Subject:* Re: [Equest-users] eQuest Error on Opening - Invalid Previous
>> Run Date
>>
>>
>>
>> Just curious, is everyone referring to or using eQuest DOE 2.3? The fixes
>> discussed have not worked for me (Doe 2.2).
>>
>> Also, this is the only content of my .ini file:
>>
>>
>>
>>
>>
>> *Jeff Ross-Bain, PE, LEED Fellow*
>>
>> President
>>
>> *Atlanta:  404-220-8955*
>>
>> *Charleston:  843-779-9229*
>>
>> *www.rbgb.com <http://www.rbgb.com/>*
>>
>>
>>
>> *From:* Equest-users <equest-users-bounces at lists.onebuilding.org> *On
>> Behalf Of *Christina LaPerle via Equest-users
>> *Sent:* Wednesday, December 17, 2025 1:13 PM
>> *To:* Rahil Shah <rahil at nyu.edu>
>> *Cc:* equest-users at lists.onebuilding.org; Melissa Crowe <
>> melissa.crowe at oakwellteam.com>
>> *Subject:* Re: [Equest-users] eQuest Error on Opening - Invalid Previous
>> Run Date
>>
>>
>>
>> Works for me too. Thanks! The key seems to be the Special= number at the
>> bottom.
>>
>>
>>
>> *Christina LaPerle (she/her)* PE, BEMP, CPHC®, CEM, CBCP
>>
>> Principal Engineer
>> ________________
>>
>> Phone 860.266.6220
>>
>> We are always looking for motivated professionals to join our team. See
>> our career options here <https://karpmanconsulting.net/available-careers>
>> !
>>
>> *PTO Alert: ** Out after 12/19/2025 and back 1/2/2025*
>>
>>
>>
>>
>>
>> On Wed, Dec 17, 2025 at 1:11 PM Rahil Shah via Equest-users <
>> equest-users at lists.onebuilding.org> wrote:
>>
>> Thanks Brian for this temporary fix. Your approach is indeed working.
>>
>> I replaced the INI file after closing equest few times. It did end up
>> opening every time.
>>
>>
>>
>> -Rahil
>>
>>
>>
>>
>>
>> On Wed, Dec 17, 2025 at 12:51 PM Brian Fountain <
>> Brian.Fountain at sa-footprint.com> wrote:
>>
>> Older (working) eQUEST.ini attached.
>>
>>
>>
>> Brian
>>
>>
>>
>> *From:* Rahil Shah <rahil at nyu.edu>
>> *Sent:* December 17, 2025 12:49 PM
>> *To:* Brian Fountain <Brian.Fountain at sa-footprint.com>
>> *Cc:* Jeff Ross-Bain <jeff at rbgb.com>; Melissa Crowe <
>> melissa.crowe at oakwellteam.com>; equest-users at lists.onebuilding.org
>> *Subject:* Re: [Equest-users] eQuest Error on Opening - Invalid Previous
>> Run Date
>>
>>
>>
>> *CAUTION: This message originated from outside Smith + Andersen*
>> ------------------------------
>>
>> Thanks Brian. Any chance you can share your old .INI, if you don't mind?
>>
>> -Rahil
>>
>>
>>
>>
>>
>> On Wed, Dec 17, 2025 at 12:46 PM Brian Fountain via Equest-users <
>> equest-users at lists.onebuilding.org> wrote:
>>
>> I am also seeing the issue.
>>
>>
>>
>> It seems to be something being written to eQUEST.ini.  I can get around
>> it by having a “clean” copy of eQUEST.ini (with a date before today’s) and
>> replacing eQUEST.ini with the clean version before opening eQUEST each
>> time. (which is still a pain but better than reinstalling)
>>
>>
>>
>> Brian
>>
>>
>>
>>
>>
>> *Footprint *
>> *Brian Fountain *Associate
>> *d *416 572 8501 m 416 562 6831
>>
>>
>>
>> *From:* Equest-users <equest-users-bounces at lists.onebuilding.org> *On
>> Behalf Of *Jeff Ross-Bain via Equest-users
>> *Sent:* December 17, 2025 11:44 AM
>> *To:* Melissa Crowe <melissa.crowe at oakwellteam.com>;
>> equest-users at lists.onebuilding.org
>> *Subject:* Re: [Equest-users] eQuest Error on Opening - Invalid Previous
>> Run Date
>>
>>
>>
>> *CAUTION: This message originated from outside Smith + Andersen*
>> ------------------------------
>>
>> Same here, including the un/install actions. The note appeared just this
>> morning!
>>
>> I also opened it once, but not again!
>>
>> Any ideas would be great!
>>
>> Thank you!
>>
>>
>>
>> *Jeff Ross-Bain, PE, LEED Fellow*
>>
>> President
>>
>> *Atlanta:  404-220-8955*
>>
>> *Charleston:  843-779-9229*
>>
>> *www.rbgb.com
>> <https://urldefense.proofpoint.com/v2/url?u=https-3A__url.ca.m.mimecastprotect.com_s_ZHoTCzvOk0U8GD5xFXhYF9oei6_&d=DwMF-g&c=slrrB7dE8n7gBJbeO0g-IQ&r=QkcMOghMp8_pF9Cam10L3g&m=t7jmYTgOF_WtRXovD5JIsbJnNTI_uJnqvKd8thpZzeKwPhft9bV4Vwe0DJJ3nBIx&s=dc-X2iocvGmZ2FK3SgNN769GxKOdEKIFrLRvgXJaoLY&e=>*
>>
>>
>>
>> *From:* Equest-users <equest-users-bounces at lists.onebuilding.org> *On
>> Behalf Of *Melissa Crowe via Equest-users
>> *Sent:* Wednesday, December 17, 2025 11:19 AM
>> *To:* equest-users at lists.onebuilding.org
>> *Subject:* [Equest-users] eQuest Error on Opening - Invalid Previous Run
>> Date
>>
>>
>>
>> Hi All
>>
>>
>>
>> I am having issues with eQuest I haven’t seen in all of my 15 years of
>> eQuest.
>>
>>
>>
>> After the first time it happened I uninstalled, reinstalled and it worked
>> 1st time but on closing eQuest and opening it back up again I get this
>> message
>>
>>
>>
>> Anyone have a fix for this?
>>
>>
>>
>>
>>
>> Thank you!!!!!!
>>
>>
>>
>> *Melissa Crowe, LEED AP, BEMP*
>>
>> *VP, Senior Mechanical Engineer*
>>
>> Oakwell
>>
>> Phone: 978-204-2559
>>
>> Email: Melissa.Crowe at oakwellteam.com
>>
>> www.oakwellteam.com
>> <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.oakwellteam.com_&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=H-N7RzYOchCli6xv70Ckr3eCssZLBe1a9sUxLbBEulo&m=yDSCSbRuLk3LBQEdF2AgzVR7PoKV--SMthczZznXG3J0a4y1ekolmT5Y6ZnHtGQF&s=N66ak3PHyJc85jfNbBc_6Vj3oaa85I3xnYl6NsUaC6o&e=>
>>
>>
>>
>> This message contains confidential information and is intended only for
>> the individual named. If you are not the named addressee you should not
>> disseminate, distribute or copy this e-mail. Please notify the sender
>> immediately by e-mail if you have received this e-mail by mistake and
>> delete this e-mail from your system.
>>
>> _______________________________________________
>> Equest-users mailing list
>>
>> https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.onebuilding.org_listinfo.cgi_equest-2Dusers-2Donebuilding.org&d=DwICAg&c=slrrB7dE8n7gBJbeO0g-IQ&r=QkcMOghMp8_pF9Cam10L3g&m=t7jmYTgOF_WtRXovD5JIsbJnNTI_uJnqvKd8thpZzeKwPhft9bV4Vwe0DJJ3nBIx&s=iJhUYEtSKygDFVKd4fcJOxZFUI2w9PlYOkQmlIdxstg&e=
>> To unsubscribe from this mailing list send  a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>> _______________________________________________
>> Equest-users mailing list
>> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to
>> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>> ------------------------------
>>
>> This email and any files transmitted with it are confidential and are
>> intended solely for the use of the individual or entity to whom they are
>> addressed. This communication represents the originator's personal views
>> and opinions, which do not necessarily reflect those of Henderson
>> Engineers, Inc. If you are not the original recipient or the person
>> responsible for delivering the email to the intended recipient, be advised
>> that you have received this email in error, and that any use,
>> dissemination, forwarding, printing, or copying of this email is strictly
>> prohibited. If you received this email in error, please immediately notify
>> administrator at hendersonengineers.com.
>>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251218/94611a45/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 27958 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251218/94611a45/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 9335 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251218/94611a45/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 49904 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251218/94611a45/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 2442 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251218/94611a45/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 9335 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251218/94611a45/attachment-0003.png>


More information about the Equest-users mailing list