[Equest-users] eQuest Error on Opening - Invalid Previous Run Date
Brian Fountain
Brian.Fountain at sa-footprint.com
Wed Dec 17 09:18:32 PST 2025
I am also seeing the issue.
It seems to be something being written to eQUEST.ini. I can get around it by having a "clean" copy of eQUEST.ini (with a date before today's) and replacing eQUEST.ini with the clean version before opening eQUEST each time. (which is still a pain but better than reinstalling)
Brian
Footprint
Brian Fountain
Associate
d 416 572 8501 m 416 562 6831
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Jeff Ross-Bain via Equest-users
Sent: December 17, 2025 11:44 AM
To: Melissa Crowe <melissa.crowe at oakwellteam.com>; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest Error on Opening - Invalid Previous Run Date
CAUTION: This message originated from outside Smith + Andersen
________________________________
Same here, including the un/install actions. The note appeared just this morning!
I also opened it once, but not again!
Any ideas would be great!
Thank you!
Jeff Ross-Bain, PE, LEED Fellow
President
Atlanta: 404-220-8955
Charleston: 843-779-9229
www.rbgb.com<https://url.ca.m.mimecastprotect.com/s/ZHoTCzvOk0U8GD5xFXhYF9oei6/>
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Melissa Crowe via Equest-users
Sent: Wednesday, December 17, 2025 11:19 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] eQuest Error on Opening - Invalid Previous Run Date
Hi All
I am having issues with eQuest I haven't seen in all of my 15 years of eQuest.
After the first time it happened I uninstalled, reinstalled and it worked 1st time but on closing eQuest and opening it back up again I get this message
Anyone have a fix for this?
[cid:image001.png at 01DC6F4E.7E0A51D0]
Thank you!!!!!!
Melissa Crowe, LEED AP, BEMP
VP, Senior Mechanical Engineer
Oakwell
Phone: 978-204-2559
Email: Melissa.Crowe at oakwellteam.com<mailto:Melissa.Crowe at oakwellteam.com>
www.oakwellteam.com<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.oakwellteam.com_&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=H-N7RzYOchCli6xv70Ckr3eCssZLBe1a9sUxLbBEulo&m=yDSCSbRuLk3LBQEdF2AgzVR7PoKV--SMthczZznXG3J0a4y1ekolmT5Y6ZnHtGQF&s=N66ak3PHyJc85jfNbBc_6Vj3oaa85I3xnYl6NsUaC6o&e=>
[cid:image003.jpg at 01DC6F4E.7E0A51D0]
This message contains confidential information and is intended only for the individual named. If you are not the named addressee you should not disseminate, distribute or copy this e-mail. Please notify the sender immediately by e-mail if you have received this e-mail by mistake and delete this e-mail from your system.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251217/84743981/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 49904 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251217/84743981/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 2442 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251217/84743981/attachment.jpg>
More information about the Equest-users
mailing list