Hi Bill,
Thank you for the link - I have watched it several times in the past. I
will be re-visiting it again however to see if I can extract more
information. As I recall it helps explain some of the inputs, but didn't
demystify the entire sizing methodology for me.
Thanks,
Chris
On Thu, Sep 12, 2024 at 9:12 AM Bill Bishop <William.J.Bishop at imegcorp.com>
wrote:
> Hi Chris,
>
>
>
> Doug Maddox worked on DOE2.3. Have you checked out his YouTube video on
> HVAC sizing? Douglas Maddox eQUEST DOE23 HVAC Sizing
> <https://www.youtube.com/watch?v=-w-nhJgjXZw>
>
>
>
> Regards,
>
> ~Bill
>
>
>
> *William Bishop*, PE, BEMP, BEAP, CEM, LEED AP
> Senior Associate / Sustainability & Energy Engineer of Distinction
>
> [image: Pathfinder | now IMEG] <https://pathfinder-ea.com/>
>
> *Pathfinder* | *now IMEG*
>
> 134 South Fitzhugh Street | Rochester, NY 14608
>
> (585) 698-1956 | phone
> (315) 879-1122 | mobile
>
> William.J.Bishop at imegcorp.com *(Please note my new email address)*
>
> *website <https://pathfinder-ea.com/> | vCard
> <https://dynasend.com/signatures/vcard/William.J.Bishop-at-imegcorp.com.vcf> | map
> <https://www.google.com/maps/place/Pathfinder+Engineers+%26+Architects+LLP/@43.1504815,-77.6145058,17z/data=!3m1!4b1!4m6!3m5!1s0x89d6b4fe9e48aab1:0x6991ae3d559d5aee!8m2!3d43.1504776!4d-77.6119309!16s%2Fg%2F1tcw955j?hl=en&entry=ttu>*
>
> [image: Twitter] <http://twitter.com/IMEGcorp>[image: spacer][image:
> Facebook] <https://www.facebook.com/IMEGcorp/>[image: spacer][image:
> LinkedIn] <https://www.linkedin.com/company/imeg-corp>
>
> Learn more
> <https://www.imegcorp.com/news_events/new-york-based-pathfinder-engineers-joins-imeg/> about
> our transition to IMEG.
>
> This email may contain confidential and/or private information. If you
> received this email in error please delete and notify sender.
>
>
>
> *From:* Equest-users <equest-users-bounces at lists.onebuilding.org> *On
> Behalf Of *Chris Hadlock via Equest-users
> *Sent:* Thursday, September 12, 2024 8:50 AM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] eQuest Sizing Methodology
>
>
>
> *External Email: *Treat links and attachments with caution.
>
> To clarify one point - I'm using eQuest 3.65 7175 DOE2.3 in my question
> below.
>
>
>
> On Wed, Sep 11, 2024 at 3:06 PM Chris Hadlock <cjhadlock at gmail.com> wrote:
>
> Fellow eQuesters,
>
>
>
> I'm looking to better understand how eQuest is using my sizing inputs to
> auto-size the heating & cooling capacities as well as airflows. In my
> example below (for a MURB in Canada), I'm modeling a PSZ system with DX
> cooling and HW heating. I've shown in the images below the (first image)
> sizing inputs from the Basics tab, the (second image) sizing inputs on the
> heating tab and (third image) the sizing outputs from the SV-C report. For
> this example, all of the values have been auto-sized based on the sizing
> inputs (and in case it matters, this system has no ventilation load):
>
>
>
>
>
> I'm looking to better understand how eQuest takes all of my inputs (and
> which inputs specifically) and derives cooling capacity, heating capacity
> and airflow for my system in question.
>
>
>
> Looking at the SV-C report and the highlight Cooling values:
>
> - How does eQuest derive the 232 cfm value (Design Day Peak airflow)?
> - How is the 6.97 MBH capacity derived? I'm assuming this is based on
> load passed onto the system, but there are clearly other system-related
> inputs that affect this value.
> - I believe the 331 cfm airflow shown as the Design Capacity Airflow
> is calculated based on my specified Rated Flow/Capacity value (7.11 MBH /
> 12 MBH/Ton * 558 cfm/Ton = 331 cfm)
>
> Looking at the Heating values in the SV-C:
>
> - How is the -8.66 MBH capacity derived? I'm assuming this is based on
> load passed onto the system, but there are clearly other system-related
> inputs that affect this value?
> - I believe the -13.49 MBH is calculated based on 331 cfm and a
> heating dT of 37.8F (331 * 37.8 * 1.085 = -13575) (I might be a little off
> with my constant value of 1.085). Does eQuest use the Heat dT specifid on
> the Basic tab or the HT-COIL-AIR-DT value I specified on the Heating Coil
> Cap tab?
>
> I would like to better understand how eQuest uses the "Heat Sup/Ret dT"
> and the "Cool Sup/Ret dT" inputs for these calculations? To further
> understand these interactions, I've run two scenarios.
>
>
>
> Scenario 1: if I reduce the Heat dT to 21F and leave the Cooling dT as
> 19.8F, I get the following output. Why does changing the Heating dT affect
> the cooling capacities? And how is the Design Heating Capacity of -15.53
> MBH determined?
>
>
>
>
>
> Scenario 2: if I reduce the Cool dT to 10F and leave the Heating dT as
> 37.8F, I get the following output.
>
>
>
>
>
> Any insights that would help me make sense of the eQuest sizing
> methodology would be appreciated.
>
>
>
> Chris
>
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20240912/d31e3cca/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 14552 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20240912/d31e3cca/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 22336 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20240912/d31e3cca/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 22469 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20240912/d31e3cca/attachment-0002.png>
More information about the Equest-users
mailing list