[Equest-users] DCV for Me, Not for Thee
Daric Adair
Daric.Adair at hendersonengineers.com
Thu Mar 23 08:52:23 PDT 2023
Bill & All;
Not to conscript your question – but an offshoot thereof. With PSZ Systems regardless of the fan and min-flow settings we have not seen the hourly airflows vary; DCV or not. Setting the fan to Constant Volume, Variable, or Fan EIR FPLR with the Min-Flow-Ratio and Min-Fan-Ratio set to 0.3 yields same hourly airflows and <1% difference in energy consumption. Checking with submetering and hourly reports. Maybe the DCV helps ‘force’ the PSZ to vary its fans?
We’ve gone to using a PVAV with an aggressive supply air temp reset (to avoid zone heating since there typically is none in this type of system). The aggressive reheat forces all the heating and cooling to the system (Where it actually is) and minimizes unmet hours.
Maybe there is an input that is being overlooked to get PSZ fans to vary, so I am all ears. I’ve cracked this up to ‘maybe they never intended for PSZ systems to have variable fans’ since eQuest/DOE has some age to it.
Any others have similar experience or workarounds ?
DARIC ADAIR
PE, BEMP, CEM
Energy Modeling Technical Manager | Energy Analyst | Associate
Venue Sector
HENDERSON ENGINEERS<https://www.hendersonengineers.com/>
Daric.Adair at hendersonengineers.com<mailto:Daric.Adair at hendersonengineers.com>
LICENSED IN KS
HENDERSON COMPANIES |
EMPLOYEE OWNED<https://www.hendersonengineers.com/employee-owned/>
From: Bishop, Bill <bbishop at pathfinder-ea.com>
Sent: Tuesday, March 21, 2023 1:52 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] DCV for Me, Not for Thee
Hey All,
Just a tip/FYI for modeling DCV. Comments, anecdotes and non-sequiturs encouraged!
I have modeled, or at least thought I modeled, demand controlled ventilation many times in eQUEST by setting the SYSTEM:MIN-OA-METHOD to DCV-RETURN-SENSOR or DCV-ZONE-SENSORS, making sure I enter the correct number of people in the spaces, using an occupancy schedule that varies, and specifying the people-based ventilation using ZONE:OA-FLOW/PER. However, I recently discovered what I believe are additional steps.
I am modeling a variable 100% OA MAU serving a laundry by entering the total OA requirement using people-based ventilation. There are 9 dryers, which I modeled as 9 people, and zone OA-FLOW/PER of 220 giving a total OA requirement of 1980 cfm for the MAU. The occupancy schedule is a good proxy for dryer use, so it should work out in principle.
I modeled the system as PSZ packaged single zone and set the SYSTEM:FAN-CONTROL to FAN-EIR-FPLR and used the ASHRAE App. G fan curve. However, the SYSTEM:MIN-FLOW-RATIO defaults to 1.0 even after setting the fan to variable control. If you adjust the SYSTEM:MIN-FLOW-RATIO to something else (let’s say 0.2) and make no other changes, the system operates at that minimum flow at all hours (and should run at higher flow to meet the thermostat setpoint if I had a higher T-stat setpoint). However, it does NOT simulate DCV.
In order to get a PSZ system to simulate DCV, you need to do all of the above PLUS set the ZONE:MIN-FLOW-CTRL to DCV-RESET-UP to allow the hourly flowrate to go above the MIN-FLOW-RATIO based on the people-based ventilation rate and schedule. You will not be able to select it from the drop-down menu, so you have to enter #SI("DCV-RESET-UP","ZONE","MIN-FLOW-CTRL") as a user expression for that zone (or zones). Now it WILL simulate DCV, as verified in the SS-L report for system fan electric energy use.
Before I figured that out, I tried modeling the system as PVAV. For the PVAV system, any value for SYSTEM:FAN-CONTROL other than CONSTANT-VOLUME gives a SYSTEM:MIN-FLOW-RATIO of no_default (no value – an empty box). CONSTANT-VOLUME gives a 1.0 MIN-FLOW-RATIO which won’t allow DCV. Regardless of which SYSTEM:MIN-OA-METHOD setting you use, including DCV-RETURN- or DCV-ZONE-SENSORS, the ZONE:MIN-FLOW-CONTROL defaults to FIXED/SCHEDULED, which will NOT simulate DCV. To simulate DCV, you have to set the ZONE:MIN-FLOW-CONTROL to DCV-RESET-DOWN. Alternatively, you can enter a ZONE:MIN-FLOW-RATIO less than 1 (say, 0.2) and set the ZONE:MIN-FLOW-CONTROL to DCV-RESET-UP.
I have not tried modeling DCV with a VAV system lately (not PVAV), but it probably requires similar inputs to the PVAV system at the SYSTEM and ZONE(s).
Any of the options above can be modified by setting the SYSTEM:MIN-AIR-SCHEDULE, which you should do regardless in most situations to model zero OA when the system is in night-cycling mode, except for a MAU which should always be 100% OA.
TL;DR version: Read the above next time you want to be confident you’re actually modeling DCV.
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[Logo, company nameDescription automatically generated] T: (585) 698-1956 www.pathfinder-ea.com<http://www.pathfinder-ea.com>
[IconDescription automatically generated][cid:image009.jpg at 01D95D75.8A52F6B0]bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>
134 South Fitzhugh Street
Rochester, NY 14608
Buffalo Office: 100 Corporate Parkway, Suite 116, Amherst, NY 14226
________________________________
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230323/0947cebd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 28877 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230323/0947cebd/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 5942 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230323/0947cebd/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 6474 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230323/0947cebd/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 5291 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230323/0947cebd/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1400 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230323/0947cebd/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.jpg
Type: image/jpeg
Size: 1289 bytes
Desc: image009.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230323/0947cebd/attachment-0003.jpg>
More information about the Equest-users
mailing list