Nicholas CATON
Nicholas.Caton at se.com
Mon Oct 10 21:36:53 PDT 2022
I'm rusty on this stuff but Ethan is absolutely on the right track!
"Loading" occurs both when you first open a project with eQuest, and as well each time you simulate the file - in each case you normally see a "loading" bar. When you have parametric runs, the BDL is "loaded" separately with the prescribed differences being implemented for each run.
I highlight/add this perspective re: when "loading" occurs to help clarify Ethan's suggestion regarding the BDL file. In each case of "loading" there should be a text file generated at that moment (timestamp), and for large projects with lots of versioning/parametric runs you may find a corresponding number of different BDL files in your project directory. You'll find warnings/errors that pop up in the loading the file will sometimes prevent simulation from happening, and sometimes won't prevent simulation. If/when you can find an ERROR in the BDL file and it isn't immediately obvious what the issue is, you can often learn a lot by considering the exact line/position of that error relative to the last-loaded model component and/or keyword, and thinking about what else in the model references that component.
Hope that's helpful!
~Nick
[cid:image001.jpg at 01D8DD76.83123E80]
Nick Caton, P.E. (US), BEMP
ニック ケートン, P.E. (US), BEMP
Senior Energy Engineer
Energy Manager, Yokota Airbase
ESS - Energy & Sustainability Services
M JP
M US
DSN
Email
+81 . 070 . 3366 . 3317
+1 . 785 . 410 . 3317
315 . 225 . 1672
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
シニアエネルギーエンジニア
横田基地エネルギーマネージャー
ESS - エナジー持続可能性サービス
[cid:image002.png at 01D8DD76.83123E80]
[cid:image003.png at 01D8DD76.83123E80]
[cid:image001.jpg at 01D8DD76.83123E80]
-----Original Message-----
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Seaman, Ethan via Equest-users
Sent: Tuesday, October 11, 2022 4:04 AM
To: PKConsulting <pasha.pkconsulting at gmail.com>; equest-users at onebuilding.org
Subject: Re: [Equest-users] Bad building component
[External email: Use caution with links and attachments]
________________________________
Hi Pasha,
A couple things come to mind, but this can be tough to diagnose without knowing the steps you took when adding the HVAC inputs. Did you only work in the eQuest user interface, or did you work in the .INP file as well?
I just had this one recently and it was coming from a single-zone system that had an incorrect thermal zone specified as it's control zone (incorrect in that the specified control zone was a thermal zone under a different system).
I recommend troubleshooting by opening the file back up with 'pause for errors' selected. That usually does a good job.
You can also open the .BDL file and search (ctrl+F) "error".
_______________________________________________
Ethan Seaman
Sustainable Design Analyst
SMMA
t: 617.520.9288
https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.smma.com%2F&data=05%7C01%7CNicholas.Caton%40se.com%7Cd2ba188ed96c43a2183f08daaaf23e97%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C638010254668154427%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=DnutJdspHgR98%2B1wcW%2F8Pw6V9ilr5UwppnERojSI0KA%3D&reserved=0
-----Original Message-----
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of PKConsulting via Equest-users
Sent: Friday, October 7, 2022 3:25 AM
To: equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: [Equest-users] Bad building component
Hi all- I just finished inputting a ton of HVAC systems and trying to run calculations and I’m getting a bad building component error- but nothing is showing up in the BDL errors and it’s not trying to run so I’m not getting a DOE2 report with an error.
Do you have any ideas on how I can find what is stopping the calcs before they even start? I’m not sure where to look to find what is causing the error? I’m not even what to look for in the inp file to find what’s not work.
I’d appreciate any ideas you have to help me push through this error to get it to calculate…
Thanks for your thoughts on this.
Pasha
Ph: 308-763-1593
_______________________________________________
Equest-users mailing list
https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=05%7C01%7CNicholas.Caton%40se.com%7Cd2ba188ed96c43a2183f08daaaf23e97%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C638010254668154427%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=DQKfIP0dYM9xxq%2BGljXMgmhAW%2BYFtSsn7NP0Hi7zcCI%3D&reserved=0
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
_______________________________________________
Equest-users mailing list
https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=05%7C01%7CNicholas.Caton%40se.com%7Cd2ba188ed96c43a2183f08daaaf23e97%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C638010254668154427%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=DQKfIP0dYM9xxq%2BGljXMgmhAW%2BYFtSsn7NP0Hi7zcCI%3D&reserved=0
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
Internal
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20221011/050f1625/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20221011/050f1625/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 1819 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20221011/050f1625/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 6024 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20221011/050f1625/attachment-0001.png>
More information about the Equest-users
mailing list