Thank you. Melissa, I think you hit the nail on the head. I am AMAZED that eQuest cannot formally do DX dual duct. Those systems certainly DO exist. Just never noticed the omission before in the program. 

    On Tuesday, June 14, 2022, 02:14:35 PM PDT, Melissa Crowe <mcrowe at cmta.com> wrote:  
 
 <!--#yiv8616268074 _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {}#yiv8616268074 #yiv8616268074 p.yiv8616268074MsoNormal, #yiv8616268074 li.yiv8616268074MsoNormal, #yiv8616268074 div.yiv8616268074MsoNormal {margin:0in;font-size:11.0pt;font-family:"Calibri", sans-serif;}#yiv8616268074 a:link, #yiv8616268074 span.yiv8616268074MsoHyperlink {color:#0563C1;text-decoration:underline;}#yiv8616268074 p.yiv8616268074MsoListParagraph, #yiv8616268074 li.yiv8616268074MsoListParagraph, #yiv8616268074 div.yiv8616268074MsoListParagraph {margin-top:0in;margin-right:0in;margin-bottom:0in;margin-left:.5in;font-size:11.0pt;font-family:"Calibri", sans-serif;}#yiv8616268074 span.yiv8616268074EmailStyle22 {font-family:"Calibri", sans-serif;color:windowtext;}#yiv8616268074 .yiv8616268074MsoChpDefault {font-size:10.0pt;} _filtered {}#yiv8616268074 div.yiv8616268074WordSection1 {}#yiv8616268074 _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {} _filtered {}#yiv8616268074 ol {margin-bottom:0in;}#yiv8616268074 ul {margin-bottom:0in;}-->
I replied too fast the multi zone is only DX will not allow CHW.
 
  
 
However this is not thermally equivalent to Dual Duct where you can cool one zone while heating the other with out reheating.
 
  
 
 
 
Melissa Crowe, BEMP, LEED AP
 
Sr Mechanical/Energy Engineer
 

 
161 Worcester Road, Suite 305
 
Framingham, MA 01701
 
O: 508.647.9200 
 
C: 978-204-2559
 
cmta.com
 

 
 
 
  
 
From: David Eldridge <DEldridge at grummanbutkus.com> 
Sent: Tuesday, June 14, 2022 5:06 PM
To: Melissa Crowe <MCrowe at cmta.com>; John Aulbach <jra_sac at yahoo.com>; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Dual Duct with package Cooling
 
  
 
|  | 
You don't often get email fromdeldridge at grummanbutkus.com. Learn why this is important
  |  |


 
 

EXTERNAL SENDER:This email originated outside of CMTA. Do not click links or open attachments unless you know the sender and know the content is safe.
 

 
 
Does it let you pick DX for the multizone AHU type?
 
  
 
David
 
  
 
  
 
David S. Eldridge, Jr., P.E., BEMP, BEAP, HBDP, GGF/A
 
Direct: (847) 316-9224 | Mobile: (773)490-5038
 
 
 
Grumman|Butkus Associates| 820 Davis Street, Suite 300 | Evanston, IL 60201
 
Energy Efficiency Consultants and Sustainable Design Engineers
 
  
 
grummanbutkus.com | Facebook | Twitter | LinkedIn
 
  
 
From: Equest-users <equest-users-bounces at lists.onebuilding.org>On Behalf Of Melissa Crowe via Equest-users
Sent: Tuesday, June 14, 2022 3:19 PM
To: John Aulbach <jra_sac at yahoo.com>;equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Dual Duct with package Cooling
 
  
 
Hi John
 
  
 
If by packaged Cooing you mean Air Cooled DX then, how about trying:
    
   - Dual Duct system w. CHW
   - “Chiller” =  Air cooled with appropriate compressor type (recip or scroll) and count
   - Pump power = 0
   - CHW supply temperature = ~ DX evaporator T
 
  
 
Good luck
 
 
 
Melissa Crowe, BEMP, LEED AP
 
Sr Mechanical/Energy Engineer
 

 
161 Worcester Road, Suite 305
 
Framingham, MA 01701
 
O: 508.647.9200 
 
C: 978-204-2559
 
cmta.com
 

 
 
 
  
 
From: John Aulbach <jra_sac at yahoo.com>
Sent: Tuesday, June 14, 2022 1:54 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Dual Duct with package Cooling
 
  
 
A friend of mine asked me about such a system. I looked it up, and lo and behold, eQuest doesn't this as a system.
 
  
 
Is there any equivalent system that can dynamically mimic this?
 
  
 
Thanks,
 
  
 
John R. Aulbach, PE
   
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/954ac603/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1901 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/954ac603/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 2025 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/954ac603/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 1796 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/954ac603/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6481 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/954ac603/attachment-0003.png>


More information about the Equest-users mailing list