Hi John
If by packaged Cooing you mean Air Cooled DX then, how about trying:
* Dual Duct system w. CHW
* “Chiller” = Air cooled with appropriate compressor type (recip or scroll) and count
* Pump power = 0
* CHW supply temperature = ~ DX evaporator T
Good luck
Melissa Crowe, BEMP, LEED AP
Sr Mechanical/Energy Engineer
[cid:image001.png at 01D8800A.7D8FBD30]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.cmta.com%2F&data=05%7C01%7CMCrowe%40cmta.com%7Cee9dc156e1f248123f2808da29e84448%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637868374796753279%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=gn955gOnIqvl6WsiUQEJ1mSVzguQnJKsZbrH4ZyxJI8%3D&reserved=0>
161 Worcester Road, Suite 305
Framingham, MA 01701
O: 508.647.9200
C: 978-204-2559
cmta.com<https://nam11.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.cmta.com%2F&data=05%7C01%7CMCrowe%40cmta.com%7Cee9dc156e1f248123f2808da29e84448%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637868374796753279%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=abW0hcCD%2BQpbv%2Bxf9bgvUZzg9r8CorSMs8fQybOtQL8%3D&reserved=0>
[cid:image002.png at 01D8800A.7D8FBD30]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2FCMTAEngineers%2F&data=05%7C01%7CMCrowe%40cmta.com%7Cee9dc156e1f248123f2808da29e84448%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637868374796753279%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=1VLG8OOlZ8is5kueNEJhZPnCujkVL14MW6OPhzGCLeA%3D&reserved=0>[cid:image003.png at 01D8800A.7D8FBD30]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Fcmta-inc.&data=05%7C01%7CMCrowe%40cmta.com%7Cee9dc156e1f248123f2808da29e84448%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637868374796753279%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=r5UGD6%2BIgCa1b6g1yAXNEAmPdLSLAphb1eM1hFBtc6k%3D&reserved=0>[cid:image004.png at 01D8800A.7D8FBD30]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2FCMTAEngineers&data=05%7C01%7CMCrowe%40cmta.com%7Cee9dc156e1f248123f2808da29e84448%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637868374796753279%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=BcV%2BFkHlCUc%2B19OYtvyyrcJY9KpbTVoM7p%2F%2F2psASn0%3D&reserved=0>
From: John Aulbach <jra_sac at yahoo.com>
Sent: Tuesday, June 14, 2022 1:54 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Dual Duct with package Cooling
A friend of mine asked me about such a system. I looked it up, and lo and behold, eQuest doesn't this as a system.
Is there any equivalent system that can dynamically mimic this?
Thanks,
John R. Aulbach, PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/dd8bb813/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6481 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/dd8bb813/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 1796 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/dd8bb813/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 2025 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/dd8bb813/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1901 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/dd8bb813/attachment-0003.png>
More information about the Equest-users
mailing list