[Equest-users] Shutting off DX cooling in winter
Nicholas CATON
Nicholas.Caton at se.com
Mon Jun 13 21:15:38 PDT 2022
Hey John!
One way to skin the cat: Under the Airside Systems tab (SYSTEM inputs), you can assign an optional cooling availability and/or heating availability schedule to limit/control the availability of either heating or cooling, independent of the fan schedule.
I don’t think this is generally limited to DX/heatpump systems - you can use the same inputs to control heating/cooling coil availability in a hydronic system as well (which would allow for something like a hydronic loop to keep circulating but have specific systems stop drawing on the associated loop).
Hope that’s helpful!
~Nick
[cid:image001.jpg at 01D87FF0.CEC47610]
Nick Caton, P.E. (US), BEMP
ニック ケートン, P.E. (US), BEMP
Senior Energy Engineer
Energy Manager, Yokota Airbase
ESS - Energy & Sustainability Services
M JP
M US
DSN
Email
+81 . 070 . 3366 . 3317
+1 . 785 . 410 . 3317
315 . 225 . 1672
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
シニアエネルギーエンジニア
横田基地エネルギーマネージャー
ESS - エナジー持続可能性サービス
[cid:image002.png at 01D87FF0.CEC47610]
[cid:image003.png at 01D87FF0.CEC47610]
[cid:image001.jpg at 01D87FF0.CEC47610]
Internal
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of John Aulbach via Equest-users
Sent: Tuesday, June 14, 2022 12:11 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Shutting off DX cooling in winter
[External email: Use caution with links and attachments]
________________________________
I know i asked this question before, but I have misplaced the answer. And i do not believe it was a thermostat control.
If i want to keep the heating going in a DX VAV system in the winter and shut down cooling, how would this be done?
The fan must keep going but the DX compressor must stop.
In a chilled water system, you can shut off the pump. But no pump exists in a DX system.
Thanks in advance.
John R. Aulbach, PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/659bcb98/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/659bcb98/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 1819 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/659bcb98/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 6024 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220614/659bcb98/attachment-0001.png>
More information about the Equest-users
mailing list