[Equest-users] Changing DHW Schedule Does not Change the Gas Consumption
Bishop, Bill
bbishop at pathfinder-ea.com
Mon Sep 27 06:14:45 PDT 2021
Hi Ahmad,
My guess is that you have entered the capacity incorrectly – a common mistake in eQUEST for boilers and DHW heaters. The units are million Btus/hour, written as MBtu/h, but MBtu/h is often interpreted the same as kBtu/h. (Boiler manufacturers often list capacities in MBH by which they mean thousands of btus per hour.)
For example, a typical 50 gallon tank water heater with a 4.5 kW electric heating element would have a capacity of (4.5kW)*(3413Btu/h-kW)/(1000000Btu/h-Mbtu/h) = 0.015 MBtu/h
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2][Logo Description automatically generated]
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image007.png at 01D7B380.1BAEB820] Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Ahmad Fraij via Equest-users
Sent: Monday, September 27, 2021 8:39 AM
To: Brian Fountain <Brian.Fountain at sa-footprint.com>
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Changing DHW Schedule Does not Change the Gas Consumption
Thanks Brian for your help. I checked the PS-H report and found that the DHW loop flow and the coil load is infinity as per the screen shot below. Do you think this is the problem? what could be the r
Warning! This message was sent from outside your organization and we are unable to verify the sender.
sophospsmartbannerend
Thanks Brian for your help.
I checked the PS-H report and found that the DHW loop flow and the coil load is infinity as per the screen shot below. Do you think this is the problem? what could be the reason?
Looking forward for your advice.
Regards
[Inline image]
On Monday, September 27, 2021, 09:47:17 PM GMT+10, Brian Fountain <brian.fountain at sa-footprint.com<mailto:brian.fountain at sa-footprint.com>> wrote:
I am not aware of a general issue with DHW in eQUEST with regards to the schedules so I suspect it is a project specific issue – at which point sharing the .inp may be helpful. I have been surprised at the impact of the UA value in the DHW heater on the heater’s efficiency, but as the loads change, the natural gas input will also.
Quick checks:
- Are the schedules linked as you expect? Daily->weekly->annual->DHW Loop Process Load
- Are the changes being masked by other gas uses? i.e. check the PS-H report in the .sim for the DHW heater – is the load and response there changing?
- Check the Process T of your DHW loop. If it is lower than the DHW loop temperature, the DHW flow is “mixed” at the tap with the incoming water temperature reducing the DHW loop flow. Perhaps this is set much too low?
[cid:image002.png at 01D7B37E.4EB70F30]
Brian
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Ahmad Fraij via Equest-users
Sent: Monday, September 27, 2021 3:51 AM
To: Fraij via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: [Equest-users] Changing DHW Schedule Does not Change the Gas Consumption
CAUTION: EXTERNAL SENDER
Hello Guys,
I am changing the fraction in the Domestics Hot Water (DHW) schedules in eQUEST but the gas consumption is not changing. Does anybody encountered something like that?
I spent a lot of time trying to fix it but I could not. Your help will be highly appreciated.
Thank you.
Ahmad
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/1d6affd6/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 78860 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/1d6affd6/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 84497 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/1d6affd6/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/1d6affd6/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 2178 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/1d6affd6/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 21586 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/1d6affd6/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 3103 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/1d6affd6/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 1554 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/1d6affd6/attachment-0003.png>
More information about the Equest-users
mailing list