[Equest-users] Changing DHW Schedule Does not Change the Gas Consumption

Ahmad Fraij fraij at yahoo.com
Mon Sep 27 05:39:10 PDT 2021


 Thanks Brian for your help.
I checked the PS-H report and found that the DHW loop flow and the coil load is infinity as per the screen shot below. Do you think this is the problem? what could be the reason?
Looking forward for your advice.
Regards



    On Monday, September 27, 2021, 09:47:17 PM GMT+10, Brian Fountain <brian.fountain at sa-footprint.com> wrote:  
 
 
I am not aware of a general issue with DHW in eQUEST with regards to the schedules so I suspect it is a project specific issue – at which point sharing the .inp may be helpful.  I have been surprised at the impact of the UA value in the DHW heater on the heater’s efficiency, but as the loads change, the natural gas input will also.
 
  
 
Quick checks:
 
-         Are the schedules linked as you expect? Daily->weekly->annual->DHW Loop Process Load
 
-         Are the changes being masked by other gas uses?  i.e. check the PS-H report in the .sim for the DHW heater – is the load and response there changing?
 
-         Check the Process T of your DHW loop.  If it is lower than the DHW loop temperature, the DHW flow is “mixed” at the tap with the incoming water temperature reducing the DHW loop flow.  Perhaps this is set much too low?
 

 
  
 
  
 
  
 
Brian
 
  
 
From: Equest-users <equest-users-bounces at lists.onebuilding.org>On Behalf Of Ahmad Fraij via Equest-users
Sent: Monday, September 27, 2021 3:51 AM
To: Fraij via Equest-users <equest-users at lists.onebuilding.org>
Subject: [Equest-users] Changing DHW Schedule Does not Change the Gas Consumption
 
  
 
CAUTION: EXTERNAL SENDER 
 
Hello Guys,
 
  
 
I am changing the fraction in the Domestics Hot Water (DHW) schedules in eQUEST but the gas consumption is not changing. Does anybody encountered something like that?
 
  
 
I spent a lot of time trying to fix it but I could not. Your help will be highly appreciated.
 
  
 
Thank you.
 
  
 
Ahmad
   
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/19f84aad/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 1632746125706blob.jpg
Type: image/png
Size: 78860 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/19f84aad/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 84497 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210927/19f84aad/attachment-0007.png>


More information about the Equest-users mailing list