[Equest-users] Limiting Equipment Runtime Hours

Bhartendu Awasthi bhartendu.awasthi90 at gmail.com
Thu Mar 18 23:12:46 PDT 2021


Dear Omer,

You can schedule your chillers based on time with the help of equipment control and load management. Please follow the following steps:

1.       Create Flag type schedules defining the chiller’s operating hours (1=ON, 0=OFF)

2.       Create two different Equipment Control for each chiller.

3.       Now, create Load Management for each of the equipment control defined above and assign the flag schedules.

I hope it will help.

 

Warm Regards,

Bhartendu Awasthi

-------------------------------------------------

LEED AP BD+C, IGBC AP, GRIHA CP

GEM CP, ECBC Design Consultant – PEDA

Energy & Sustainability Consultant

National Capital Region-New Delhi, India

S: bhartendu_awasthi

L: bhartenduawasthi

 

From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ömer Moltay via Equest-users
Sent: Friday, March 19, 2021 1:45 AM
To: equest-users at onebuilding.org
Subject: [Equest-users] Limiting Equipment Runtime Hours

 

Dear All,

I have an absorption chiller and compression chillers in an office building, where the absorption chiller would run during daytime and compression chillers during night time.

How would you have eQuest do this? Can I specify runtime schedules for different equipment?

Thank you in advance,

Ömer Moltay, LEED AP BD+C, ASHRAE BEMP, ASHRAE CPMP
Mimta EcoYapi, LEED Proven Provider
Hekimsuyu Cad. 559. Sk.
No:39 34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
Mobile: 90-533-957-1394
www.eco-yapi.com <http://www.eco-yapi.com> 
www.buildingenergymodels.com <http://www.buildingenergymodels.com/>  

    

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210319/79bf75a1/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 44049 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210319/79bf75a1/attachment-0003.png>


More information about the Equest-users mailing list