[Equest-users] Unable to generate ANY .CSV file in eQuest

Nicholas CATON Nicholas.Caton at se.com
Tue Mar 16 01:07:43 PDT 2021


Hi John,

Are you referencing the Every Good Modeler Educates the Uninformed Every Day file?  (“… _EG_MoEU_ED.csv”)

Fresh install of 3.65, build 7175.  I’m getting that file generated with a dummy model using doe 2.2 engine:
[cid:image001.png at 01D71A85.E1E59110]

And… also with the doe 2.3 engine:
[cid:image005.png at 01D71A86.59B6A1C0]

If this is the file you are looking for, then I am curious whether you might also be having trouble viewing the “rainbow reports” from within the interface, after a simulation?
[cid:image006.png at 01D71A86.CEC16680]

I may be mis-remembering, but possibly the CSV under discussion is tied to the generation of these views so there might be something to explore there on your end?

If all else fails and you need a fast workaround, File > Export > Hourly results will net you a csv with default meter hourly reporting data which would be suitable to extract/sum anything you might have otherwise pulled from the “every good modeler” csv.

~Nick

[cid:image002.jpg at 01D71A85.E1E59110]
Nick Caton, P.E. (US), BEMP
ニック ケートン, P.E. (US), BEMP
Senior Energy Engineer
Energy Manager, Yokota Airbase
ESS - Energy & Sustainability Services
M JP
M US
Email
+81 . 070 . 3366 . 3317
+1   . 785 .  410  . 3317
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
シニアエネルギーエンジニア
横田基地エネルギーマネージャー
ESS - エナジー持続可能性サービス

[cid:image003.png at 01D71A85.E1E59110]
[cid:image004.png at 01D71A85.E1E59110]
 [cid:image002.jpg at 01D71A85.E1E59110]


From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of John Aulbach via Equest-users
Sent: Friday, March 12, 2021 1:00 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Unable to generate ANY .CSV file in eQuest


[External email: Use caution with links and attachments]

________________________________


A .CSV file used to pop up automatically when i ran. Now it does not. I have changed NOTHING in the .INI file.

Any idea what gives? Using 3.65 Build 7175.

Thanks !!

john

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/ebd0da83/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 23187 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/ebd0da83/attachment-0015.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/ebd0da83/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 1947 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/ebd0da83/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 6510 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/ebd0da83/attachment-0017.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 23680 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/ebd0da83/attachment-0018.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 65600 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/ebd0da83/attachment-0019.png>


More information about the Equest-users mailing list