[Equest-users] Rooftop Control
Nicholas CATON
Nicholas.Caton at se.com
Mon Mar 15 22:14:14 PDT 2021
I cannot recall dabbling with this in recent memory, but I think you might want to read up on the staged-capacity/staged-volume PVVT system options in the doe2 reference.
Volume 2: Dictionary<mk:@MSITStore:C:\Users\sesa399002\Documents\eQUEST%203-65%20Data\Help\DOE22\DOE-2.chm::/Docs/volume2dictionary.htm> > HVAC Components<mk:@MSITStore:C:\Users\sesa399002\Documents\eQUEST%203-65%20Data\Help\DOE22\DOE-2.chm::/Docs/hvaccomponents.htm> > SYSTEM<mk:@MSITStore:C:\Users\sesa399002\Documents\eQUEST%203-65%20Data\Help\DOE22\DOE-2.chm::/Docs/system1.htm> > Staged Flow/Capacity DX Cooling/Heating Systems
Reviewing the help files, it looks like there are a few options for sequencing that are actually constant volume with 2+ stages of cooling, engaged in response to discharge temperature. This would appear to be one step removed from return air monitoring as posed, but in line with the concept of varying your mechanical cooling energies in response to aggregate load conditions.
~Nick
[cid:image002.jpg at 01D71A6D.7EC81C00]
Nick Caton, P.E. (US), BEMP
ニック ケートン, P.E. (US), BEMP
Senior Energy Engineer
Energy Manager, Yokota Airbase
ESS - Energy & Sustainability Services
M JP
M US
Email
+81 . 070 . 3366 . 3317
+1 . 785 . 410 . 3317
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
シニアエネルギーエンジニア
横田基地エネルギーマネージャー
ESS - エナジー持続可能性サービス
[cid:image003.png at 01D71A6D.7EC81C00]
[cid:image004.png at 01D71A6D.7EC81C00]
[cid:image002.jpg at 01D71A6D.7EC81C00]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Chapin, Alex N via Equest-users
Sent: Saturday, March 13, 2021 3:07 AM
To: Ömer Moltay <omoltay at mimtarch.com>; equest-users at onebuilding.org
Subject: Re: [Equest-users] Rooftop Control
[External email: Use caution with links and attachments]
________________________________
Hi Ömer,
One way to do this would be to merge all of the zones/spaces into one. There may be a way to do what you want without merging zones, but nothing is coming to mind. Good luck
Alex Chapin PE, BEMP, LEED AP BD+C, O+M
Energy Engineer | Mason & Hanger
A Day & Zimmermann Company
O 804.521.7072
4880 Sadler Road, Suite 300 | Glen Allen, VA 23060
masonandhanger.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.masonandhanger.com%2F&data=04%7C01%7CNicholas.Caton%40se.com%7Cd9b3f81cf92d48b6696d08d8e5847654%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C1%7C637511704385274520%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=vmVFSrc8T8%2BRt12UbU7bP%2FfWtrj2P%2BpuTcfFHPMF2Do%3D&reserved=0>
An ISO 9001 Certified Company<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.masonandhanger.com%2Fabout%2Fiso&data=04%7C01%7CNicholas.Caton%40se.com%7Cd9b3f81cf92d48b6696d08d8e5847654%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C1%7C637511704385274520%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=gm0LIYb8AFFWjyEIUoKgEkWIVwyw2DVpFxKkh13iFb4%3D&reserved=0>
Building a More Secure World ®
CAUTION - THIS EMAIL MAY CONTAIN CONFIDENTIAL INFORMATION
This electronic mail transmission and any accompanying documents may contain information belonging to the sender, which may be proprietary, confidential, and/or otherwise subject to restrictions on disclosure beyond the intended recipient. This information is intended only for the use of the individual or entity to whom this electronic mail transmission was sent as indicated above. If you are not the intended recipient, any disclosure, copying, distribution, or action taken in reliance on the contents of the information contained in this transmission is strictly prohibited. If you have received this transmission in error, please call 1-703-955-5702 and delete this transmission. Thank you.
From: Ömer Moltay [mailto:omoltay at mimtarch.com]
Sent: Wednesday, March 10, 2021 5:49 PM
To: equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: [Equest-users] Rooftop Control
Dear All,
If a constant volume rooftop is controlled with a thermostat located in a zone, then we have to use either PSZ or PVVT systems to define its control zone.
How would one model a control where the rooftop supply air temperature setpoint is set according to the return air temperature (ie. average of zone temperatures)?
Thank you in advance,
Ömer Moltay, LEED AP BD+C, ASHRAE BEMP, ASHRAE CPMP
Mimta EcoYapi, LEED Proven Provider
Hekimsuyu Cad. 559. Sk.
No:39 34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
Mobile: 90-533-957-1394
www.eco-yapi.com<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__http%3A%2Fwww.eco-yapi.com__%3B!!EsbUyp2cb-_kIuQ!rWQYJNrJpGIUk8sP-G1Gcpys_GivQ5NzTnq3cvhjoRxtpyOww2IU32AxPXVvYc7gDkLbEkI%24&data=04%7C01%7CNicholas.Caton%40se.com%7Cd9b3f81cf92d48b6696d08d8e5847654%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C1%7C637511704385284475%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=1XQX0rPPJB2MnKAH7CU5Yg9ooMv3ewuXwkZ0unQDtQY%3D&reserved=0>
www.buildingenergymodels.com<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Furldefense.com%2Fv3%2F__http%3A%2Fwww.buildingenergymodels.com%2F__%3B!!EsbUyp2cb-_kIuQ!rWQYJNrJpGIUk8sP-G1Gcpys_GivQ5NzTnq3cvhjoRxtpyOww2IU32AxPXVvYc7g3aUtilg%24&data=04%7C01%7CNicholas.Caton%40se.com%7Cd9b3f81cf92d48b6696d08d8e5847654%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C1%7C637511704385284475%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=zfAlMgPL0h8lboZKrTzpSrYOYtfmuir6B7CafwJn370%3D&reserved=0>
[cid:image005.png at 01D71A6D.7EC81C00]
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/816150de/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/816150de/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 1947 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/816150de/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 6510 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/816150de/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 44049 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210316/816150de/attachment-0011.png>
More information about the Equest-users
mailing list