[Equest-users] Weather info Download issues

Jeff Ross-Bain jeff at rbgb.com
Thu Jun 24 07:31:36 PDT 2021


Hi All,

Not sure if this is valid, but I have had the same error when trying to get a new weather file.
Do you have MS 365? I do and have noticed that a new "documents" folder is created (in MS 365) which seems to take priority over the normal C-drive "documents" folder (eQuest looks to the C-drive folder for data).
When I try to get a new weather file in eQuest, I think the site tries to access the MS 365 folder (not the C-drive) and gets confused.
I now manually copy the weather file, place it in the C-drive eQuest weather folder, and all works.
Is this something that others have experienced?

Jeff Ross-Bain, PE, LEED Fellow, MSc, BCxP, BEMP
President
Charleston:  843-779-9229
Atlanta:  404-220-8955
www.rbgb.com<http://www.rbgb.com/>

Maximizing Building Performance


From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Seaman, Ethan via Equest-users
Sent: Thursday, June 24, 2021 9:59 AM
To: Cory Pierce <cory.pierce at clarkenersen.com>
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Weather info Download issues

Hi Cory,

I can't help you with the HTTP response error, but perhaps this workflow could prove useful.

You mentioned being able to download and import weather files manually.  Anecdotally, I keep a shortcut to the TMY3 folder on my desktop, and have https://doe2.com/Download/Weather/TMY3/ bookmarked on my browser.  This has always allowed me to quickly access and set up the weather file I need.

Good luck with the server response issue, I wish I could be more help with that.

_______________________________________________
Ethan Seaman
Sustainable Design Analyst
SMMA
t: 617.520.9288
www.smma.com<http://www.smma.com>

From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Cory Pierce via Equest-users
Sent: Wednesday, June 23, 2021 4:56 PM
To: 'equest-users at lists.onebuilding.org' <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: [Equest-users] Weather info Download issues

Having some issues getting Weather data to download in eQuest.

Program installs and launches fine.

If we try to download weather data we get an error stating "Failed to receive a valid HTTP response from the server".

If we manually download the weather data it downloads successfully and we can manually import the data in eQuest.

Wondering if anyone else has experienced this or has some ideas of how we can get it working successfully.

F.Y.I.  eQuest is running on a Windows10 laptop, 64Gb memory, 512 SSD, Corei7, Dedicated graphics.

Thanks

Cory Pierce
Director of Information Technology
Associate Principal

o  402.477.9291
e  cory.pierce at clarkenersen.com<mailto:cory.pierce at clarkenersen.com>
w clarkenersen.com<http://www.clarkenersen.com/>

1010 Lincoln Mall, Suite 200, Lincoln, NE 68508-2883

[cid:image001.png at 01D768E4.1BC70920]

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210624/8bbbf8d6/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 8622 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210624/8bbbf8d6/attachment.png>


More information about the Equest-users mailing list