[Equest-users] Gas-fire radiant heater
Integral Mechanical Engineering Designs
integralmech at outlook.com
Mon Jan 25 15:48:13 PST 2021
Hi Bill,
I will consider and check the data according your suggestion.
Thanks for the help,
Paul
From: Bishop, Bill<mailto:bbishop at pathfinder-ea.com>
Sent: January 25, 2021 11:21 AM
To: Integral Mechanical Engineering Designs<mailto:integralmech at outlook.com>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] Gas-fire radiant heater
Hi Paul,
I suggest modeling a gas-fired radiant heater as a unit heater with HEAT-SOURCE = FURNACE. If you want to try determining energy savings compared to convective heaters, there have been posts here and on Bldg-Sim with suggestions such as using different thermostat setpoints based on occupant comfort, or splitting up high-bay spaces into conditioned and unconditioned zones.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2][Logo Description automatically generated]
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image005.png at 01D6F31C.E7F5D550] Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Integral Mechanical Engineering Designs via Equest-users
Sent: Monday, January 25, 2021 11:58 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Gas-fire radiant heater
Hi all,
Does somebody know if it is possible to model gas-fire radiant heaters like the one in this link?
https://www.dropbox.com/s/4yyyzfyct2pqezn/IMG_9013.JPG?dl=0
Kind Regards,
Paul
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210125/7dfc860c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 1554 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210125/7dfc860c/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: E979774F0D3646C9BE3775297390523A.jpg
Type: image/jpeg
Size: 2966 bytes
Desc: E979774F0D3646C9BE3775297390523A.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210125/7dfc860c/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 8B994E257D2F4A77A1EB450409462209.png
Type: image/png
Size: 7728 bytes
Desc: 8B994E257D2F4A77A1EB450409462209.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210125/7dfc860c/attachment-0007.png>
More information about the Equest-users
mailing list