Good morning John,

It is indeed easy and that is exactly what I use Global Parameters for.

[cid:image001.png at 01D6E730.7D317CD0]

In the example I currently have open, I have a global parameter named “Infiltration multiplier”.

I use the abbreviation #PA to refer to the global parameter in a user expression.  (You can also spell out Parameter).  You need double quotes around the global parameter name.  Spaces are fine in the parameter name but capitalization is important.  In the user expression I multiply the zone infiltration by #PA(“Infiltration multiplier”).

[cid:image002.png at 01D6E730.7D317CD0]

In this example, I have a parametric run that cuts the infiltration in half by setting “Infiltration multiplier” to 0.5.

[cid:image003.png at 01D6E731.809D8930]

I hope this helps and that you are doing well.

Cheers,
Brian

Footprint

Brian Fountain
Associate


From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of John Aulbach via Equest-users
Sent: Saturday, January 9, 2021 3:43 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Global Parameters

CAUTION: EXTERNAL SENDER
I have never done global parameters before in eQuest. Is it possible to place a multiplier holder next to each CFM in a 50 AHU run, then place a 0.7 in parametrics so that all fans are reduced by 30%?

Hope it is easy.

JOhn
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210110/46f8d6bd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 2419 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210110/46f8d6bd/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 39981 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210110/46f8d6bd/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 12452 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210110/46f8d6bd/attachment-0011.png>


More information about the Equest-users mailing list