[Equest-users] Variable Chilled Water Supply Temperature
Daric Adair
Daric.Adair at hendersonengineers.com
Thu Apr 1 07:45:34 PDT 2021
You indicated Loop > Controls > Cooling > Setpoint Control > Fixed . Id also clear out any Reset Schedule Inputs if there in there. Leftover/ghost inputs can mess with us sometimes.
Also check Loops > Operation > Loop Operation > Standby/Demand/Snap. This has caused issues for us in the past when not set properly
Might also run hourly report to see if there are any demands on loop from coils for cooling when the temperature has floated up. If no demands, then CHW temperature may not matter.
Thanks,
DARIC ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst
HENDERSON ENGINEERS<https://www.hendersonengineers.com/?utm_source=hei&&utm_medium=email&&utm_campaign=hei-shortsignature>
daric.adair at hendersonengineers.com<mailto:daric.adair at hendersonengineers.com>
LICENSED IN KS
HENDERSON PROUD SINCE 1970<https://www.hendersonengineers.com/about-us/our-story/?utm_source=hei&utm_medium=email&utm_campaign=hei-shortsignature> | JUST GETTING STARTED.
From: Nitin Harjai <nitin.harjai28 at gmail.com>
Sent: Thursday, April 1, 2021 7:57 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Variable Chilled Water Supply Temperature
Hi everyone,
I have created a customized hourly report for chillers to understand the supply water temperature of screw chillers. It was observed that the leaving temperature is varying from 44°F to 65°F which is quite high.
This seems very strange as the set-point cooling control is fixed and the set point cooling temperature is 44°F under the chilled water loop. Also I have considered the loop set point range as zero (0). As per the inputs entered under the chilled water loop, the supply chilled water temperature should be near around 44°F.
Can anyone guide me on this, why the supply water temperature of the chiller is varying and how I can fix this?
Thanks in advance.
________________________________
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20210401/d1c7f141/attachment.htm>
More information about the Equest-users
mailing list