[Equest-users] Simulation Error - Abnormal simulation results detected - Sim Guidelines

Bishop, Bill bbishop at pathfinder-ea.com
Tue Sep 15 08:31:11 PDT 2020


Hi Ethan,
Thank you for the reference to the Mass. Simulation Guidelines. There are some helpful eQUEST-specific tips and keyword expressions in there!
FYI - there is a newer version v2.3 released July 2020. Not sure how different it is. https://www.masssave.com/-/media/Files/PDFs/Business/Hourly_Simulation_Guidelines.pdf?la=en&hash=B4A511B16BCBE4B2FCB286C4A92F84B479A39851
Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer

[Pathfinder-EA-logo-2]T: (585) 698-1956                        F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>        www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608               [cid:image004.png at 01D68B53.B5B235B0]         Ask me why Carbon Fee & Dividend may be right for you.

From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Seaman, Ethan via Equest-users
Sent: Tuesday, September 15, 2020 9:47 AM
To: equest-users at lists.onebuilding.org; Lee Shaver <lshaver at slipstreaminc.org>; Kathryn Kerns <kathryn.kerns at bceengineers.com>
Subject: Re: [Equest-users] Simulation Error - Abnormal simulation results detected

Lee,

Great idea - thank you!

Kathryn,

If possible, could you 'save as' the current model, and restore your former model to a previous save as date from when you got the error? It'd then be possible to look at both before and after .inp files side-by-side.  If not I understand.

All,

The HVAC system I'm using is an active chilled beam system (work-around) detailed here (MA PA Guidelines 2017 doc):

https://www.masssave.com/-/media/Files/PDFs/Business/MA-PA-Simulation-Guidelines-v22.pdf?la=en&hash=C8AE342C6E058B301659FABE59A098C0C0F43CF8

In my case MassSave is the reviewer, so we have to use their system work-around.

I have a feeling that this error may come down to the heating and cooling design days, perhaps more specifically the weekend HDD/CDDs introduced in DOE 2.3.  I've only been able to find one resource that outlines design days in eQuest (Doug Maddox's video/slides).

_______________________________________________
Ethan Seaman
Sustainable Design Analyst
SMMA
t: 617.520.9288
www.smma.com<http://www.smma.com>

From: Lee Shaver <lshaver at slipstreaminc.org<mailto:lshaver at slipstreaminc.org>>
Sent: Monday, September 14, 2020 9:16 PM
To: Kathryn Kerns <kathryn.kerns at bceengineers.com<mailto:kathryn.kerns at bceengineers.com>>; Seaman, Ethan <eseaman at smma.com<mailto:eseaman at smma.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: Simulation Error - Abnormal simulation results detected

Kathryn,

Any chance you saved the before and after *.inp files? Would be interesting to diff them and see what actually changed.

Lee Shaver
Project Manager
he/him/his<https://nam04.safelinks.protection.outlook.com/?url=https%3A%2F%2Fslipstreaminc.org%2Fabout%2Fdiversity-inclusion&data=02%7C01%7Clshaver%40slipstreaminc.org%7C4e393111db174a58290708d7fb7f24e4%7C14e9186db92e4c6db3d654b54c168413%7C1%7C0%7C637254395807699483&sdata=vCaR8%2F2HTfqa4RpeT%2F0Epa7cTRMpnvWV1uKopNZlVHE%3D&reserved=0>

608.210.7145
lshaver at slipstreaminc.org<mailto:lshaver at slipstreaminc.org>
[A picture containing drawing  Description automatically generated]<https://nam04.safelinks.protection.outlook.com/?url=https%3A%2F%2Fslipstreaminc.org%2F&data=02%7C01%7Clshaver%40slipstreaminc.org%7C4e393111db174a58290708d7fb7f24e4%7C14e9186db92e4c6db3d654b54c168413%7C1%7C0%7C637254395807709478&sdata=9jpwp0B0wxlmtOsJWSDZOoydw8Uk9Vk5c7965IfDkNE%3D&reserved=0>

From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Kathryn Kerns via Equest-users
Sent: Monday, September 14, 2020 7:08 PM
To: Seaman, Ethan <eseaman at smma.com<mailto:eseaman at smma.com>>
Cc: 'equest-users at lists.onebuilding.org' <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>>
Subject: Re: [Equest-users] Simulation Error - Abnormal simulation results detected

This happened to me too just today. The only way I got out of it was to recreate the PVAV system from scratch,  assign all the zones to the new system and then delete the PVAV that I was adjusting when the error suddenly appeared. No idea what happened.

From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Seaman, Ethan via Equest-users
Sent: Monday, September 14, 2020 12:31 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Simulation Error - Abnormal simulation results detected

Hi eQuest-users,

I've lurked here for a while learning from many of you, and am hoping this group's collective experience can help get me out of this pickle.

First off, I'm modeling in eQuest 3.65 7175 - DOE 2.3.

The error I'm getting reads as such from the output report:

***ERROR***********************************************************************
             Abnormal simulation results detected. Please
             send this input and weather file to program developers.
             MsgBomb call argument:      2010  12-7   1/ 1/ 2  HDD

***ERROR***********************************************************************
             Abnormal simulation results detected. Please
             send this input and weather file to program developers.
             MsgBomb call argument:      2010  12-7   1/ 1/ 2  Hol

I believe it has something to do with the heating design day, or the fan schedule, but everything I've tried as far as troubleshooting hasn't gotten my any further to being able to simulate the model.

This same error was once discussed here before, but this modeler's solution doesn't work the same on my model. http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/2019-May/005994.html<https://nam04.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Fpipermail%2Fequest-users-onebuilding.org%2F2019-May%2F005994.html&data=02%7C01%7Clshaver%40slipstreaminc.org%7Ccc8d79495aed40658d2008d8590b6451%7C14e9186db92e4c6db3d654b54c168413%7C1%7C0%7C637357252753834529&sdata=L8Ch%2BjPHj3Kqw35ru4GA1Nn64qsLO5KsnFRQM9l6o%2BE%3D&reserved=0> This modeler suggests changing the fan schedule from ON/OFF/FLAG to ON/OFF which alone does not solve my sim error.

Attached is a zipped folder with the .inp, .pd2, .bdl, and tmy3 file.

Thank you, and god bless!
_______________________________________________
Ethan Seaman
Sustainable Design Analyst
SMMA
1000 Massachusetts Avenue, Cambridge, MA 02138
t: 617.520.9288
eseaman at smma.com<mailto:eseaman at smma.com>
LinkedIn<https://nam04.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.linkedin.com%2Fcompany%2Fsmma-symmes-maini-%26-mckee-associates%3Ftrk%3Dcp_followed_name_smma-symmes-maini-%2526-mckee-associates&data=02%7C01%7Clshaver%40slipstreaminc.org%7Ccc8d79495aed40658d2008d8590b6451%7C14e9186db92e4c6db3d654b54c168413%7C1%7C0%7C637357252753834529&sdata=wQVVhKJeDpbodN5tvJpV3X%2BUoapwFamXyrGkqjguTos%3D&reserved=0> | Twitter<https://nam04.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2Fsmma_design&data=02%7C01%7Clshaver%40slipstreaminc.org%7Ccc8d79495aed40658d2008d8590b6451%7C14e9186db92e4c6db3d654b54c168413%7C1%7C0%7C637357252753844522&sdata=areCg%2FKvg0uZ5bZEcZcQfnL04nVqyVhK2dzJsWE%2FYiw%3D&reserved=0> | Instagram<https://nam04.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.instagram.com%2Fsmma_design%2F&data=02%7C01%7Clshaver%40slipstreaminc.org%7Ccc8d79495aed40658d2008d8590b6451%7C14e9186db92e4c6db3d654b54c168413%7C1%7C0%7C637357252753844522&sdata=Hf11vG%2FxwPwddgsKoCX6bRJGjDrp7A7nX993KpkHS4Q%3D&reserved=0>
www.smma.com<https://nam04.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.smma.com%2F&data=02%7C01%7Clshaver%40slipstreaminc.org%7Ccc8d79495aed40658d2008d8590b6451%7C14e9186db92e4c6db3d654b54c168413%7C1%7C0%7C637357252753854518&sdata=LeXhiC0qwkH4O8a8AgAWXEYEl6J%2FU9R61ewQY3bNt4E%3D&reserved=0>


CAUTION: This email originated from outside the Slipstream organization. Do not click on links or open attachments unless you recognize and trust the sender.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200915/25d39c66/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2047 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200915/25d39c66/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200915/25d39c66/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1903 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200915/25d39c66/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1554 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200915/25d39c66/attachment.png>


More information about the Equest-users mailing list