[Equest-users] eQUEST infiltration rate
Nicholas Caton
Nicholas.Caton at se.com
Fri Oct 30 07:06:31 PDT 2020
I am not as read up on this matter as I have been in years past*, but I think an important thing to consider here is that 90.1 is prescribes envelope leakage corresponding to pressures typical of blower door tests, which in turn reflect pressures corresponding to rather extreme weather (wind velocity) conditions. Concurrently, eQuest is set to normalize infiltration around more modest wind pressures, with intent to allow natural ventilation to vary with hourly windspeed data from the weather BIN. Apples and oranges, in a sense.
I’ve attached messages from a prior [equest-users] thread, with contributions from myself and Keith Swartz. If ever someone were equipped/able to update the doe2 reference manual and provide commentary around infiltration inputs relative to 90.1 prescriptions and real-world envelope airtightness testing… they might find these to be a helpful resource =).
Kind regards!
~Nick
* At one point, in the course of one of the lowdown showdown competitions, I worked on developing a excel tool to bridge eQuest infiltration inputs and real-world blower testing results. That involved reading up a lot on blower testing methodology and how envelope airtightness is prescribed/executed in different municipalities and countries around the world. This entailed a sort of “literature review” of prescriptive standards / green building standards / etc… If I learned anything, it was that this is a hard sort of tool to build that isn’t ultimately region/standard specific (down to an AHJ level), as variances in how blower test performances are performed/recorded can generate very different ideas of what constitutes good/acceptable/poor levels of infiltration for prescriptive purposes. This was however a number of years ago and it’s possible some national/international consistency may have developed (particularly among jurisdictions where infiltration testing is done with some regularity). I’d love to hear from anyone in such an area who has “figured out” a defensible approach to marrying real-world blower testing (with specific methodology) to energy model inputs.
[cid:image003.jpg at 01D6AF11.46A43600]
Nick Caton, P.E. (US), BEMP
Senior Energy Engineer
Energy Manager, Yokota Airbase
ESS - Energy & Sustainability Services
M US
M JP
Email
785 . 410 . 3317
… TBD …
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219 USA
ニック ケートン, P.E. (US), BEMP
シニアエネルギーエンジニア
横田基地エネルギーマネージャー
ESS - エナジー持続可能性サービス
M US
M JP
Email
785 . 410 . 3317
… TBD …
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219 USA
[cid:image004.png at 01D6AF0E.797DD160]
[cid:image005.png at 01D6AF0E.797DD160]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Daric Adair via Equest-users
Sent: Wednesday, October 28, 2020 10:39 PM
To: Phil Jordan <phil.jordan at clearesult.com>; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQUEST infiltration rate
[External email: Use caution with links and attachments]
________________________________
The 0.038 cfm/ft2 is the Wizard Default. We typically override it to a higher value, but not to 0.4 cfm/sf. That’s at a pressure well above typical building pressurization. We’ve used 0.04 and 0.05 in the past with no questions asked. ASHRAE 90.1-2016 G3.1.1.4 has defined a method to determine the infiltration rate.
Thanks,
DARIC ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst
HENDERSON ENGINEERS<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hendersonengineers.com%2F%3Futm_source%3Dhei%26%26utm_medium%3Demail%26%26utm_campaign%3Dhei-shortsignature&data=04%7C01%7CNicholas.Caton%40se.com%7C437513de1c964654e74708d87b46dfba%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C1%7C637394891615815268%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=zAAhclDuid4et3AldgFLC%2FhPIj9dZ2ir9wutbA4k0UQ%3D&reserved=0>
daric.adair at hendersonengineers.com<mailto:daric.adair at hendersonengineers.com>
LICENSED IN KS
From: Phil Jordan <phil.jordan at clearesult.com<mailto:phil.jordan at clearesult.com>>
Sent: Monday, October 26, 2020 11:15 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] eQUEST infiltration rate
Is that the default the wizard uses? I believe it’s been 0.4 cfm/ft2 (@ 0.3 in. of water) for the past few cycles of 90.1 at least (Section 5.4.3).
Regards,
Phil Jordan
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Lapierre, Patrick via Equest-users
Sent: Monday, October 26, 2020 9:09 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] eQUEST infiltration rate
EXTERNAL email. Please exercise caution. This e-mail is from a sender outside of CLEAResult. Do not click any links or open any attachments from unknown senders or unexpected email. ***************************************************
Hello all,
Does anyone remember where in ASHRAE is referenced the default value for infiltration (0.38 cfm/ft2) that eQUEST uses?
I can’t seem to trace it back, yet I’m pretty sure it comes from ASHRAE.
Thank you,
[cid:image006.jpg at 01D6AF0E.797DD160] <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.bpa.ca%2F&data=04%7C01%7CNicholas.Caton%40se.com%7C437513de1c964654e74708d87b46dfba%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C1%7C637394891615825262%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=a280uuG8T%2F9Yo2In%2BamB4z75MsZFfiCwPn95N6k%2Fsww%3D&reserved=0>
Patrick Lapierre_ing. BEMP, Chargé de projets
Développement durable et Efficacité énergétique
plapierre at bpa.ca<mailto:plapierre at bpa.ca> | www.bpa.ca<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.bpa.ca%2F&data=04%7C01%7CNicholas.Caton%40se.com%7C437513de1c964654e74708d87b46dfba%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C1%7C637394891615825262%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=a280uuG8T%2F9Yo2In%2BamB4z75MsZFfiCwPn95N6k%2Fsww%3D&reserved=0> | t: 5143833747x2807
Carrières<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.bpa.ca%2Fcarriere&data=04%7C01%7CNicholas.Caton%40se.com%7C437513de1c964654e74708d87b46dfba%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C1%7C637394891615835257%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=NVL8Nog2LfhTEmM2AUmpZ4QSEeqKgTevD6z4d6AYOUA%3D&reserved=0>
Avertissement / Disclaimer
Les informations contenues dans le courriel que vous venez de recevoir, y compris les pièces jointes, sont destinées à l’usage exclusif de la (ou des) personne(s) identifiée(s) comme destinataires et sont confidentielles. Si vous n’en êtes pas le destinataire, soyez avisé que tout usage en est interdit. Si vous avez reçu ce courriel par erreur, veuillez le retourner à l’expéditeur et le supprimer complètement de votre système informatique.
The information contained in this communication from the sender is confidential. It is intended solely for use by the recipient and others authorized to receive it. If you are not the recipient, you are hereby notified that any disclosure, copying, distribution or taking action in relation of the contents of this information is strictly prohibited and may be unlawful.
This email has been scanned for viruses and malware, and may have been automatically archived.
________________________________
This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com<mailto:administrator at hendersonengineers.com>.
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201030/bd8e8843/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1947 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201030/bd8e8843/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 6510 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201030/bd8e8843/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 13484 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201030/bd8e8843/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201030/bd8e8843/attachment-0001.jpg>
-------------- next part --------------
An embedded message was scrubbed...
From: Nicholas Caton <Nicholas.Caton at se.com>
Subject: Re: [Equest-users] Infiltration inputs
Date: Wed, 30 Mar 2016 21:56:25 +0000
Size: 54010
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201030/bd8e8843/attachment.mht>
-------------- next part --------------
An embedded message was scrubbed...
From: Keith Swartz <KSwartz at seventhwave.org>
Subject: Re: [Equest-users] Infiltration inputs
Date: Fri, 1 Apr 2016 21:09:57 +0000
Size: 57904
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201030/bd8e8843/attachment-0001.mht>
More information about the Equest-users
mailing list