[Equest-users] eQUEST infiltration rate

Daric Adair Daric.Adair at hendersonengineers.com
Wed Oct 28 06:39:04 PDT 2020


The 0.038 cfm/ft2 is the Wizard Default. We typically override it to a higher value, but not to 0.4 cfm/sf. That’s at a pressure well above typical building pressurization. We’ve used 0.04 and 0.05 in the past with no questions asked. ASHRAE 90.1-2016 G3.1.1.4 has defined a method to determine the infiltration rate.

Thanks,
DARIC ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst

HENDERSON ENGINEERS<https://www.hendersonengineers.com/?utm_source=hei&&utm_medium=email&&utm_campaign=hei-shortsignature>
daric.adair at hendersonengineers.com<mailto:daric.adair at hendersonengineers.com>

LICENSED IN KS

From: Phil Jordan <phil.jordan at clearesult.com>
Sent: Monday, October 26, 2020 11:15 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQUEST infiltration rate

Is that the default the wizard uses? I believe it’s been 0.4 cfm/ft2 (@ 0.3 in. of water) for the past few cycles of 90.1 at least (Section 5.4.3).

Regards,

Phil Jordan

From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Lapierre, Patrick via Equest-users
Sent: Monday, October 26, 2020 9:09 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] eQUEST infiltration rate

EXTERNAL email. Please exercise caution. This e-mail is from a sender outside of CLEAResult. Do not click any links or open any attachments from unknown senders or unexpected email. ***************************************************
Hello all,

Does anyone remember where in ASHRAE is referenced the default value for infiltration (0.38 cfm/ft2) that eQUEST uses?
I can’t seem to trace it back, yet I’m pretty sure it comes from ASHRAE.

Thank you,


  [cid:image001.jpg at 01D6AD04.F73023D0] <https://nam12.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.bpa.ca%2F&data=04%7C01%7Cphil.jordan%40clearesult.com%7C922b1ea6029c41fc47bd08d879c97b84%7Cc505a74550c6477fa1107be89b513acc%7C1%7C0%7C637393253562115145%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=VPNlBW3wH2ut04ohxLoqGoZ%2FAl6RTkjd9Yv5fv3kXiY%3D&reserved=0>
Patrick Lapierre_ing. BEMP, Chargé de projets
Développement durable et Efficacité énergétique
plapierre at bpa.ca<mailto:plapierre at bpa.ca>   |  www.bpa.ca<https://nam12.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.bpa.ca%2F&data=04%7C01%7Cphil.jordan%40clearesult.com%7C922b1ea6029c41fc47bd08d879c97b84%7Cc505a74550c6477fa1107be89b513acc%7C1%7C0%7C637393253562115145%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=VPNlBW3wH2ut04ohxLoqGoZ%2FAl6RTkjd9Yv5fv3kXiY%3D&reserved=0>  |  t: 5143833747x2807
Carrières<https://nam12.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.bpa.ca%2Fcarriere&data=04%7C01%7Cphil.jordan%40clearesult.com%7C922b1ea6029c41fc47bd08d879c97b84%7Cc505a74550c6477fa1107be89b513acc%7C1%7C0%7C637393253562125142%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=BvVZikOpcTN%2B9VzqIOWU%2FdISKGwffyyCwvPeodiETxA%3D&reserved=0>



Avertissement / Disclaimer

Les informations contenues dans le courriel que vous venez de recevoir, y compris les pièces jointes, sont destinées à l’usage exclusif de la (ou des) personne(s) identifiée(s) comme destinataires et sont confidentielles. Si vous n’en êtes pas le destinataire, soyez avisé que tout usage en est interdit. Si vous avez reçu ce courriel par erreur, veuillez le retourner à l’expéditeur et le supprimer complètement de votre système informatique.

The information contained in this communication from the sender is confidential. It is intended solely for use by the recipient and others authorized to receive it. If you are not the recipient, you are hereby notified that any disclosure, copying, distribution or taking action in relation of the contents of this information is strictly prohibited and may be unlawful.

This email has been scanned for viruses and malware, and may have been automatically archived.

________________________________

This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201028/463ed32a/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 13484 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201028/463ed32a/attachment.jpg>


More information about the Equest-users mailing list