I’m not sure but I don’t think you can apply a default expression to any TYPE keyword – whether it’s for a DW-heater, a SYSTEM, a SCHEDULE etc.
One alternative is to create multiple DHW heaters, and modify the default expression for CAPACITY to vary with the value of #PA(“DHW_Type”), so that the types you don’t want to use have a .001 capacity.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2][Logo Description automatically generated]
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image005.png at 01D6A77D.57714540] Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of samuel mason via Equest-users
Sent: Tuesday, October 20, 2020 10:53 PM
To: Equest Users Mailing List <Equest-users at lists.onebuilding.org>
Subject: [Equest-users] User Expression for DHW heater type
Hello,
I am trying to set up a user expression for the type of DHW heater in a project. When I use the symbolic index control shown below and add it directly into the equest interface, the model runs fine and the graphical interface shows the correct heater type.
However, when I save the model, the INP file does not get written with the #SI notation and when I reload the model, it crashes while loading the BDL right when it gets to the DW-heater. Does anyone know how to get around this?
Snippet:
TYPE =
{IF(#PA("DHW_Type")==1) THEN
#SI("GAS","DW-HEATER","TYPE")
ELSE IF (#PA("DHW_Type")==2) THEN
#SI("ELEC","DW-HEATER","TYPE")
ELSE IF(#PA("DHW_Type")==3) THEN
#SI("HEAT-PUMP","DW-HEATER","TYPE")
ELSE
#SI("GAS","DW-HEATER","TYPE")
ENDIF
ENDIF
ENDIF}
DHW_Type is a global parameter of type numeric.
I also tried putting this code into the default for the DW-heater with a user expression and this also crashes when trying to load the BDL.
Thank you in advance.
Sam
Sam Mason P.E., LEED AP BD+C, BEMP
Principal
Encompass Energy, LLC
P: 443-410-1534
E: sam.mason at encompassenergyLLC.com<mailto:sam.mason at encompassenergyLLC.com>
W: www.encompassenergyLLC.com<http://www.encompassenergyLLC.com>
This e-mail and all contents are CONFIDENTIAL and intended only for the recipient(s) to whom it is addressed. Any use of the information by anyone other than the intended recipient is prohibited
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201021/e81c1a39/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201021/e81c1a39/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2178 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201021/e81c1a39/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 21586 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201021/e81c1a39/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 3103 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201021/e81c1a39/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 1554 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201021/e81c1a39/attachment-0001.png>
More information about the Equest-users
mailing list