[Equest-users] Reverting from DOE- 2.3 to 2.2

Brian Fountain Brian.Fountain at sa-footprint.com
Fri May 15 06:52:12 PDT 2020


With regards to opening a file started in 2.3 in 2.2, there are 4 LOADS keywords that have parentheses around them in 2.3 and not in 2.2.  They are:



o   PEOPLE-HG-LAT

o   PEOPLE-HG-SENS

o   NUMBER-OF-PEOPLE

o   AREA/PERSON



You can either edit the .inp file with a text editor and remove the parentheses for these keywords or set these keywords to default in 2.3 before opening the file in 2.2.  I also recommend setting the space occupancy schedules to default in 2.3 before opening in 2.2.



Note - before fixing these keywords, I often find the file opens in 2.2 with spaces missing so the result looks catastrophic.



At the system level, the OA-FLOW/PER also has parentheses around it in 2.3 and not 2.2.  There are other system keywords that don't translate but I have found as long as I fix the LOADS keywords mentioned above, I can open a 2.3 file in 2.2 and then make any required system/plant keyword fixes.  Depending on how the chiller efficiency is specified in 2.3, I have seen the chillers drop to the bottom of the component tree in 2.2.



With the reverse change (adding parentheses in the .inp or defaulting the listed keywords), a 2.2 file will open OK in 2.3 in my experience.





Cheers,



Brian



Footprint

Brian Fountain P.Eng., LEED AP BD+C, BEMP
Associate
d 416 572 8501 m 416 562 6831
Brian.Fountain at sa-footprint.com

1100 - 100 Sheppard Ave. East, Toronto ON M2N 6N5
t 416 218 7025   f 416 487 9104   sa-footprint.com

VANCOUVER  |  CALGARY  |  EDMONTON  |  WINNIPEG  |  KITCHENER  |  TORONTO   |   OTTAWA

Please reconsider printing this email. Help sustain our resources.

This e-mail and attachments are CONFIDENTIAL and intended only for the recipient to whom it is addressed. If you are not the intended recipient, please notify the sender and delete all copies immediately. Any use of the information herein by anyone other than the intended recipient is prohibited



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200515/6a81639d/attachment.html>


More information about the Equest-users mailing list