When you say loads, do you mean the end-use energy breakdown totals? (Loads = heat/cooling gains in the spaces – VFDs should not be affecting heating or cooling loads.)
If the change to the tower fan motors allows a different control of the condenser water temperature to be colder water then the compressor energy of the individual heat pumps would go down.
David
David S. Eldridge, Jr., P.E., BEMP, BEAP, HBDP, GGA
Associate
Direct: (847) 316-9224 | Mobile: (773) 490-5038
Grumman/Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201
Energy Efficiency Consultants and Sustainable Design Engineers
grummanbutkus.com<http://grummanbutkus.com/> | Blog<http://grummanbutkus.com/blog> | Facebook<https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526> | Twitter<https://twitter.com/grummanbutkus>
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Dilshad Ahmed Khan via Equest-users
Sent: Monday, May 11, 2020 3:00 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Impact of Cooling Tower EEM on Space Cooling load
Hello everyone!
I have modeled water cooled packaged DX systems that are connected to a cooling tower having a single-speed fan and pump. When I change the single-speed fan and pump with variable speed drives as an EEM, the results show a reduction in "Pumps & Aux." load as well as "Space Cooling" load. In fact, sometimes the reduction in space cooling load seems to be greater than "Pumps & Aux." load itself. Can anybody decipher what is the relation of VSDs pump and fan of cooling tower with space cooling load?
Thanks