[Equest-users] Chiller sequencing with respect to outdoor temperature

Nicholas Caton Nicholas.Caton at se.com
Mon May 11 06:29:41 PDT 2020


It’s gonna be a good week!

Sequencing chiller based on outdoor temperature.


  1.  Behold, a dummy model wherein I’ve entered detailed mode and changed the default names for a pair of chillers to something easy to copy a few times here:

[cid:image001.png at 01D62764.A51DBA10]

  1.  Prompt:  I want CH-A to handle the loop for all conditions where the outdoor drybulb temperature is less than or equal to 85F.  I want CH-B only to handle the loop at all other times.
  2.  Looking downwards in my component tree, while in the water-side HVAC tab, I observe an empty component group entitled “Equipment Control.”  Right-click that, and “Create Equipment Control…”

[cid:image005.png at 01D62765.047B54E0]

  1.  At the prompt, give this Equipment Control a name that reflects your intent in the moment.  Choose the Control Type based on the kind of equipment you are trying to control (reference article pasted here for convenience), and select a Loop to which this applies if prompted as well:

[cid:image009.png at 01D6276E.4B1743B0]

[cid:image007.png at 01D62765.9F422260]

  1.  Navigate to the Load Range 1 tab, select CH-A in the first dropdown, and enter nothing for the capacity (which is interpreted by the program to mean there is no limit on this first phase of operation.  Note that I did not also list CH-B, so this should effectively isolate operation to only CH-A while this EQUIP-CTRL is active.

[cid:image018.png at 01D6276B.A6D10B30]

  1.  A general aside:  For any other real-world sequence with more complex elements like multiple chillers/boilers/etc running at the same time… I can’t write a quick/simple guide for something that broad, but you’d be well advised to skim the reference materials under Volume 2: Dictionary<mk:@MSITStore:C:\Users\sesa399002\Documents\eQUEST%203-65-7175%20Data\Help\DOE23\DOE-2.chm::/Docs/volume2dictionary.htm> > HVAC Components<mk:@MSITStore:C:\Users\sesa399002\Documents\eQUEST%203-65-7175%20Data\Help\DOE23\DOE-2.chm::/Docs/hvaccomponents.htm> > EQUIP-CTRL<mk:@MSITStore:C:\Users\sesa399002\Documents\eQUEST%203-65-7175%20Data\Help\DOE23\DOE-2.chm::/Docs/equipctrl1.htm> … and specifically Volume 2: Dictionary<mk:@MSITStore:C:\Users\sesa399002\Documents\eQUEST%203-65-7175%20Data\Help\DOE23\DOE-2.chm::/Docs/volume2dictionary.htm> > HVAC Components<mk:@MSITStore:C:\Users\sesa399002\Documents\eQUEST%203-65-7175%20Data\Help\DOE23\DOE-2.chm::/Docs/hvaccomponents.htm> > EQUIP-CTRL<mk:@MSITStore:C:\Users\sesa399002\Documents\eQUEST%203-65-7175%20Data\Help\DOE23\DOE-2.chm::/Docs/equipctrl1.htm> > TYPE = COOLING<mk:@MSITStore:C:\Users\sesa399002\Documents\eQUEST%203-65-7175%20Data\Help\DOE23\DOE-2.chm::/Docs/typecooling.htm> for sequencing chillers
  2.  Now back out of these inputs, right click the freshly created EQUIP-CTRL in the component tree, and copy it.  Give it a distinct name and change the CH-A assignment to CH-B:

[cid:image006.png at 01D6276B.F82EF820]

  1.  Now we just need to define under which circumstances we should use either EQUIP-CTRL.  Right click the empty component group “Load Management” in the component tree, and the first prompt will allow you to name and select a load management type.  If you select OA Temperature, you’ll be prompted to provide a temperature to correspond with your first sequence.  You can more descriptively think of this as “the maximum temperature for the first range of operation.”  Once again, if it’s initially unclear you can always change this stuff up later.

[cid:image012.png at 01D62768.CACF17A0]

[cid:image008.png at 01D6276B.F82EF820]

  1.  Click through your management sequence tabs, and select your EQUIP-CTRL intended for each range of temperatures.  Once again, there are a lot of input options available to accommodate a diversity of sequence intents, worthy of review pretty much anytime you are engaging these input dialogs, but for this prompt our lives are pretty simple:

[cid:image015.png at 01D6276B.F82EF820]

[cid:image020.png at 01D6276B.F82EF820]

  1.  We’re almost done!   This is probably the most universally important step.  Any time you mess with EQUIP-CTRL and LOAD-MANAGEMENT, I’d advise it’s easy enough for anybody to get turned around with the input options at-hand.  Set up a custom hourly report to track the operations of the targeted equipment, to help yourself verify intent and tweak inputs as necessary down the line.  I’m skipping through those steps as it’s something I and others have covered many times before on the lists (see archives if needed).  In this case, I’m just going to generate two columns of chiller loading alongside the hourly OADB conditions:

[cid:image013.png at 01D6276A.6458B4C0]

  1.  Simulate and export custom hourly report to confirm results/intent.  Spend a little time here to make the visual pretty / intuitive as it probably belongs in an imaginary report somewhere… this is where we earn our keep after all ;-)

[cid:image010.png at 01D6276E.4B1743B0]

In this case I’m using pivot chart/table to quickly slice down to the first week of June, where I can observe weather conditions that should trigger between CH-A and CH-B.  Seems satisfactory to me!



I hope this helps you and others dipping your toes into sequencing with eQuest!   This is a relatively deep rabbit hole / skillset, but your prompt felt like an appropriately simple enough sequence to set up an introductory example for the community… Thanks for asking!

~Nick


[cid:image011.jpg at 01D6276E.4B1743B0]
Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Energy and Sustainability Services
  Energy Performance Contracting
D
M
E

913 . 564 . 6361
785 . 410 . 3317
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219

[cid:image004.png at 01D62764.A51DBA10]


From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Arnab Saha via Equest-users
Sent: Sunday, May 10, 2020 1:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Chiller sequencing with respect to outdoor temperature


[External email: Use caution with links and attachments]

________________________________


Dear equest users,

I am currently modelling an adiabatic chiller for large commercial complex.

For this particular design, I need to do load management and chiller sequencing between air cooled and water cooled chiller on basis of outdoor air temperature.
Please provide a suitable path for this modelling.

Regards
ARNAB SAHA


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 44720 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0026.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 8477 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0027.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 52466 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0028.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 26318 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0029.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.png
Type: image/png
Size: 10548 bytes
Desc: image012.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0030.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.png
Type: image/png
Size: 19416 bytes
Desc: image013.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0031.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image018.png
Type: image/png
Size: 15976 bytes
Desc: image018.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0032.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 26221 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0033.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 5293 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0034.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image015.png
Type: image/png
Size: 35351 bytes
Desc: image015.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0035.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image020.png
Type: image/png
Size: 33955 bytes
Desc: image020.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0036.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 23890 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0037.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 47409 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0038.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.jpg
Type: image/jpeg
Size: 1793 bytes
Desc: image011.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200511/8577840f/attachment-0002.jpg>


More information about the Equest-users mailing list